Table 4D2A (page 334). Multicore 70°C thermoplastic insulated and sheathed cables.

Reference Method B (enclosed in conduit on a wall or in trunking etc.​)

Thks Jud, but I think we must be getting crossed wires somewhere mate. I'm talking about flat twin and earth, 70'C thermoplastic insulated and sheathed flat cable with pc, Table 4D5 p340. Your talking about multicore 70'C thermoplastic insulated sheathed cable, 4D2A p334 which is the round flex cable used in things like kettle or extension leads. It's a different type of cable to flat T&E which is why they have separate pages. Also in the Green Unite book page 159 it says Table 4D5- Flat T+E? Thks
 
Thks Jud, but I think we must be getting crossed wires somewhere mate. I'm talking about flat twin and earth, 70'C thermoplastic insulated and sheathed flat cable with pc, Table 4D5 p340. Your talking about multicore 70'C thermoplastic insulated sheathed cable, 4D2A p334 which is the round flex cable used in things like kettle or extension leads. It's a different type of cable to flat T&E which is why they have separate pages. Also in the Green Unite book page 159 it says Table 4D5- Flat T+E? Thks

Tables 4F1A onwards (page 350) are for flexible cables.

T&E is still a Multicore thermoplastic insulated and sheathed cable.

Table 4D5 is the install methods for T&E in contact with thermal insulation.
 
Last edited by a moderator:
Tables 4F1A onwards (page 350) are for flexible cables.

T&E is still a Multicore thermoplastic insulated and sheathed cable.

Table 4D5 is the install methods for T&E in contact with thermal insulation.


Ahh! Thks mate, glad uve explained tht, im happy now knowing im doing something tht does comply. cheers
 
T&E is still a Multicore thermoplastic insulated and sheathed cable.

Table 4D5 is the install methods for T&E in contact with thermal insulation.

You'd think that the current carrying capacity for reference method C for both tables 4D2A and 4D5 would be the same in that case wouldn't you?
Unless the slight difference is due to flat versus round with flat being slightly better at dissipating heat?
 
The only consideration i'd have to using mini trunking (or PVC conduit to some extent) in a commercial kitchen, is on the environmental side of things. eg, ...routing to avoid heat damage, oil and grease build-up and the like!!! Which when you consider the usual abysmal overall installation workmanship of mini trunking systems can be considerable, ...a vermin's paradise!! lol!!
 
The only consideration i'd have to using mini trunking (or PVC conduit to some extent) in a commercial kitchen, is on the environmental side of things. eg, ...routing to avoid heat damage, oil and grease build-up and the like!!! Which when you consider the usual abysmal overall installation workmanship of mini trunking systems can be considerable, ...a vermin's paradise!! lol!!


Agree, iv already told them iv gotta take down the trunking already in place, as its just the adhesive type and is falling off the walls. I like the adhesive trunking only because it seals around the screws i add to hold it on the walls lol.
Im lucky as the cooker is going in a far corner so heat shouldnt be a problem where im routing/cooker switch. Grease is there problem, but tbf they are an upmarket coffee shop/cafe and are really on the ball with being clean. Their daughter also live upstairs so they keep the place clean for her kid.
 

Reply to T&E in mini trunking in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Indeed, that was my thought, a B20 having a 60A instantanious trip should easily cover a inrush for a domestic fridge, and if the fridge and...
Replies
11
Views
555
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top