Hello Folks,
Currently I am wiring a customers kitchen and diner.
We're using 1mm T+E for Lighting
6mm for cooker, 2.5 for everything else.
He is filling the ceilings with thermal/acoustic insulation after wiring and before the ceilings go up.
Now then, Table 4D5 states the following current carrying capacities for ref method 103
1mm = 8A
6mm = 23.5A
2.5mm = 13.5A
Surely I dont have to derate this by half because of the thermal insulation??
Also, customer want downlighters. Am I right in saying that the only downlighters he can have where the themal insulation is going to cover them are Aurora's SOLA range?
Cheers!