Hi all can some one help me out with this,

It = In divided ccxcixcgxca

I have a 32 amp mcb divided by cc 1 x cg 0.80 x ca 1.03 = 38.8 amps current carrying capacity.

What would the tabulated current carrying capacity be, as it should be higher than the current carrying capacity.

Hope that's not to confusing,

Thanks chris
 
For a ring you work out Ib and multiply this by 1.67 to get your protective device. This is In. You then find It, by dividing Ib by the derating factors (Cg, Ci, Cg, Ca and finally 0.725 if a 3036 fuse).You then have a provisional conductor size. Check this with the following, max mv/a/m = max vd/ (length x Ib). You look down the tables and find a conductor with a mv/a/m figure less than this. You then need to check thermal withstand and disconnection times. You also need to select or calculate a CPC.
 
so say 26A for standard A1 ring circuit x by 1.67=44A protective device 45A . so then 26A/0.725x0.9= 40A so say clipped direct t&e would equal 6mm for (It) for volt drop you 7.3x 26 x100m/1000/4= 5V as vd... but this is 6mm (It)
 

Reply to the thread, titled "Tabulated current carrying capacity" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top