Hi every one how are u all on this nice monday morning. I wanted to ask i was at a job today and noticed that the tails from the meter to the consumer unit was in 10mm twin and earth and they was using the earth from the twin and earth to be the main earth From the cu and i did not think it is right and i suggested that they change the tails for 16 mm armoured cable ( i know u suppost to put 22mm tails in now but i though seen as it is a small flat 16 would be ok) and 10 mm earth cable it is a flat with 1 lighting circuit 1 ring final circuit and 1 cooker circuit and it is about 14 meter run from the meter to the consumer unit is this right or am i totally wrong any advice would be good
 
Remember the t&e will be protected by the switch fuse so that will govern how much current the t&e will take.
Rather than 'tails' (they are the bits between the meter and the switch fuse) think of it as a submain - there is additional protection provided by the switch fuse so you're not just relying on the service fuse for that length.
As regards reference method, presumably you wouldn't have a problem installing t&e that way for a socket, so why a submain? Unless it is a TT earthing system it wouldn't necessarily need rcd protection either, due to the age of the installation.
 
he could put in 25mm tails rather than 16mm if he wanted to, as long as the supply fuse protects the tails then its all good, if the distance from the meter to the CU is a really long run, up a riser for example then Id say armoured would be better, although prob more expensive cost wise, depends if they are willing to pay the additional costs, labour and material for the install, I agree tho the 10mm twin is undersized and is a pile of rubbish, if the cpc of the t+e has been used as the main earth then this needs ripping out quickly and a seperate 16mm earth running in its place.
Hope this helps you mate and good luck with it.
 
ah ok missed the TT bit :)
thanks

and on the size of he earth (16mm) if he installed it, why would this matter ??

on a TT, your resistance should be under 200 ohms , if he wanted to put in an earth cable that was 125mm that would be ok (apart from look strange )
As long as the earth isnt undersized.

Cant see why replacing the CPC from the cut out to the CU would be a bad thing ?
Yes ensure this meets the disconnection time, but why wouldnt a 16mm earth from the cut out to the CU mean the disconnection time wasnt met?
 
Last edited by a moderator:
Llloyd you could use spent Dilithium Crystals from the Warp Drive of the SS Enterprise if you are so inclined, as long as by Adiabatic equation proves it will carry the fault current.

But what you can't do is advise someone that a T + E sub main on a TT installations need ripping out quick and a 16mm installed, as if that T+E is going to suddenly explode into a roaring inferno, there is no need for a 16mm main earthing conductor on a TT system, and so why advise someone that is the minimum requirements as it isn't
 
My point was not that the 10mm would suddenly explode haha , my point was that the cpc of the 10mm twin and earth would be too small and would need to have its size increased,
for a disconnection time to be met you would need an acceptably low impedence path back to earth, this would increase the fault curent and trip the disconnect in a faster time.
The larger an earthing conductor the easier it is for the fault curent to pass through (low resistance) and then the fault current spike increases in direct relation to the impedance.
So the higher the impedance the lower the fault current and the slower the disconnect will go, breaker tripping or fuse blowing,
So the lower the impedance the higher the fault current and the faster the disconnect will go, breaker tripping or fuse blowing.
I know my stuff when it comes to this so you cant tell me that leaving the CPC of a peice of 10mm twin and earth as the main earth conductor (TT system or whatever flipping system ) will be more beneficial to a disconnection time than replacing it with a 16mm seperate earth.

Maybe they taught you to use spent dilythiam crystals from the warp drive in college

They just taught me to use copper cable, dont think any wholesaler I know stocks spent dilythiam crystals or warp drives?
Maybe its a new square D range ?
 
My point was not that the 10mm would suddenly explode haha , my point was that the cpc of the 10mm twin and earth would be too small So you know that, you have done the equation and it's too small .....fair enough and would need to have its size increased,
for a disconnection time...........We are talking earthing conductors here not R1 + R2, remember the disconnection times are met by both conductors not purely the size of your earth to be met you would need an acceptably low impedence path back to earth, this would increase the fault curent and trip the disconnect in a faster time.......you seemed to have grasped that
The larger an earthing conductor the easier it is for the fault curent to pass through (low resistance) and then the fault current spike increases in direct relation to the impedance.
So the higher the impedance the lower the fault current and the slower the disconnect will go, breaker tripping or fuse blowing,
So the lower the impedance the higher the fault current and the faster the disconnect will go, breaker tripping or fuse blowing.
I know my stuff when it comes to this ......Do you so you cant tell me that leaving the CPC of a peice of 10mm twin and earth as the main earth conductor (TT system or whatever flipping system ) will be more beneficial to a disconnection time than replacing it with a 16mm seperate earth..............Yes I can if I prove it by calculation

Maybe they taught you to use spent dilythiam crystals from the warp drive in college....................not sure what they taught you

They just taught me to use copper cable, dont think any wholesaler I know stocks spent dilythiam crystals or warp drives?
Maybe its a new square D range ?[/QUOTE

Well I'll have to bow to your obvious expertise on this
 

Reply to Tail size from meter to cu in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
705
  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
684

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top