Got to replace a CU in a flat this week, question is do I need to upgrade the tails?

TNC-S, supply runs from meter in common cupboard on GF, into 60a fused isolator, then from there in 16mm T&E.

I am going to upgrade the main earth and bonding to services to 16mm and 10mm respectively but unsure what I am required to do qith the tails on this one. Distance from Isolator to CU is prob about 12m.

Thanks in advance :)
 
IMO as the 16mm sub is protected by a 60A switchfuse at the origin it's fine, no need to upgrade. Unless theres going to be an increase in load in the flat or something requiring the 60A fuse to be upgraded.
 
Cheers Lenny, would you upgrade earth from switchfuse to CU then or leave as is and just upgrade from Earth block to switchfuse??
 
I'm thinking its 6mm, its the earth from the twin, so I will upgrade it to 16mm, bigger the better as they say.

Thanks again mate :)
 
An adiabatic may prove the 6mm to be sufficient.......up to you though.

If you are going down the new earth road though, a 16mm will be more than adequate.:)
 
Are you sure you have a 60A re-wireable???

For a correct calc you would need the measured Zs, You can use a best case scenario by using the max Zs for the pretective device though.
 
Last edited by a moderator:
Lets give it a bash then.

Obviously as you are using the max Zs, the fault current will be at it's lowest yes....


So, 230V/1.12 = 205.35A, which gives a "T" of 5s

205.35 x 205.35 = 42168.6

42168.6 x 5 = 210843.

Sqrt of 210843 = 459.17.

459.17 / 115 = 3.99mm.


As I said, if the measured Zs is lower.....which it should be, the fault current will be higher.
 
Last edited by a moderator:

Reply to Tails for flat in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
726

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top