Boy's Whats the ruling on tails longer than 3m less than 8,Is a switch Fuse required or is it down to the suppliers requirements, I dont understand the need for a Sw/fuse as the cable is 25mm SWA
 
Boy's Whats the ruling on tails longer than 3m less than 8,Is a switch Fuse required or is it down to the suppliers requirements, I dont understand the need for a Sw/fuse as the cable is 25mm SWA

Is your 5 key broken
[ElectriciansForums.net] Tails
[ElectriciansForums.net] Tails
 
Last edited by a moderator:
usually i would fit anything from 2m as that seems to be the common minimum between dno's and saves messing on ringing around trying to find someone capable to give you the correct answer.
 
just reading the post, surely if you are putting a fused isolator in line then I would assume you would down rate it, i.e, 100A mian cut out, 80A at isolator?
without looking in the books, could you not get away with a smaller csa than 25mm, reduce costs etc.

Ross.
 
The distributor’s cut-out fuse, or switch, if one is provided, may be used to isolate meter tails and other equipment immediately downstream, subject to the distributor’s agreement.
A condition of the distributor’s agreement is often a restriction on the length of the meter tails, perhaps to as little as one or two metres.
This means that, where the main distribution board or switchboard is too far from the electricity supply meter to be supplied by the maximum allowed length of tails, an additional linked switch or linked circuit-breaker has to be provided, to act as the main switch for the installation.
Like any main switch, the additional switch or circuit-breaker should be located as near as practicable to the origin of the installation (the meter) as required by Regulation 537.1.4.

Note, however, that distributors generally do not permit consumer’s equipment such as a main switch to be located on their meter board or within their meter cabinet.
 
Indeed, it is a question for your DNO as they do vary between them.

SSE or as they are now know as Southern Electric (again) will only gurantee fault protection on the first three meters (internal) and 4 meters external, after which a switchfuse must be installed.
 

Reply to Tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
605
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
936

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top