I was shown how to take the Ze from a domestic installation, at collage last week.
I have forgot how to do it, where to connect the probes of the MFT, and weather or not to disconnect the earth.
I need to know before Friday.
Can anybody go through it? would be better with diagrams.

Thanks would appreciate.
 
I was shown how to take the Ze from a domestic installation, at collage last week.
I have forgot how to do it, where to connect the probes of the MFT, and weather or not to disconnect the earth.
I need to know before Friday.
Can anybody go through it? would be better with diagrams.

Thanks would appreciate.

Broadly..... (and depending on MFT to some extent)....

Ensure that it is safe to remove the main earth from the system - ISOLATE THE SUPPLY FIRST.

Then it's a case of connecting the earth lead to the incoming earth (having made sure all other earths are disconnected)
Live to live, neutral to neutral

MFT to lowest Ohm setting, and hit the button.

Erm.... do you not have a GN3?
 
Google 'earth fault loop impedance test' I'm sure somewhere u will find a guide with diagrams.

Do you not have a college book or college notes? U should get some if your serious about learning the subject. For testing, there is a book called part p doctor which goes through testing step by step with clear diagrams.

Think about what it is your trying to measure, the impedance external to the installation (the supply side) so you need to test at the incoming point of the DB.

I could continue to go through it step by step, but I'm not sure it will help you. The best way to learn testing is not to know how to do it, but discover what your actually measuring and for what purpose. Get your head into a book or a website finding out what your measuring and why and what the impact of the result is.

Good luck, it ain't that hard tbh.

Tom
 
External earth loop impedance (Ze) test - YouTube

this ones good, explains the test but on a 3 phase install, on single phase obviously you only have one incoming line
where as this chap is testing 3 lines in and doubling the highest of the two.
dont forget to fasten earth back into the bar.

so tnc-s your max stated .35 ohm
tns max .8 ohm
tt 200 ohm

give your croc clip a good squeeze and push the line probe hard onto the incoming line.

- - - Updated - - -

http://www.youtube.com/watch?v=PUTn3t65na4

this ones good, explains the test but on a 3 phase install, on single phase obviously you only have one incoming line
where as this chap is testing 3 lines in and doubling the highest of the two.
dont forget to fasten earth back into the bar.

so tnc-s your max stated .35 ohm
tns max .8 ohm
tt 200 ohm

give your croc clip a good squeeze and push the line probe hard onto the incoming line.
 
turn off supply to installation, remove earthing conductor, but you might have to prove isolated before emoving earthing conductor .... and so on..

that book is pretty easy to follow and has pictures...
 
The test itself is really easy but remember safe isolation procedure and to re-connect the earthing conductor before switching the power back on
 

Reply to Taking the Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top