Can someone please teach me how to do a proper cable calculation, step by step would be really really appreciated so i can learn and know for future.

It will be a standard house TN-C-S system
The run is going to be 30meters
It will be clipped along a wall and tied to a cantenary wire then into a garage

I need to work out what size cable i will need
What type of cable
What size breaker i will need

Kind Regards
Dave
 
Using his calculation for my board outside with 1 double socket and 2 fluorescent lights of a 360 pir is roughly 4000 Watt (about 3800)

TN-C-S
30meters

Step 1
4000 watts / 230 volts = 17.39

Step 2
20 Amp breaker

Step 3
Cg = No grouping single cable
Ci = No insulation clipped direct outside
Ca = 30 degree (outside) = 1
Cf = not a bs3036 its a bs60898 so = 1

so 20 / 2 = 10 ??


Dont get
STEP 4. Select cable size fromBS 7671 App 4. (Iz/t) > (In) > (Ib).
(Iz/t) = ________amps
From table __________ Reference Method __________ Cable size = _______mm##

I ONLY HAVE AN ON SITE GUIDE (ANY IDEA WHAT PAGE TO FIND THE ABOVE)but it looks like 1.5mm2 from a table i did find Clipped direct (20a)

Step 5
30meters x 17.39 x 29 / 1000 = 15.12 volts max is 9.6 so 1.5 not good

2.5 is 30 x 17.39 x 18 / 1000 = 9.39 volts which is below the max 9.6

So if i was to INSTALL this cable chosen 4mm rather than 2.5mm in the chance he wants more sockets or an auto garage door etc

4mm 3 Core NYY-J Cable Black
4mm 3 Core NYY-J Cable Black

That would be good enough to run from his mains-board inside out along a wall and wire into garage to a mainsboard?? from a 20A breaker (Upgrade to 32A breaker incase of upgrade)

Cheers
 
Using his calculation for my board outside with 1 double socket and 2 fluorescent lights of a 360 pir is roughly 4000 Watt (about 3800)

TN-C-S
30meters

Step 1
4000 watts / 230 volts = 17.39

Step 2
20 Amp breaker OK

Step 3
Cg = No grouping single cable = 1
Ci = No insulation clipped direct outside = 1
Ca = 30 degree (outside) = 1
Cf = not a bs3036 its a bs60898 so = 1

so 20 / 2 = 10 ?? Wrong....20 Ă· (1 x 1 x 1 x 1) = 20


Dont get
STEP 4. Select cable size fromBS 7671 App 4. (Iz/t) > (In) > (Ib).
(Iz/t) = ________amps
From table __________ Reference Method __________ Cable size = _______mm##

Choose a cable that can carry at least 20A

I ONLY HAVE AN ON SITE GUIDE (ANY IDEA WHAT PAGE TO FIND THE ABOVE)but it looks like 1.5mm2 from a table i did find Clipped direct (20a)

Step 5
30meters x 17.39 x 29 / 1000 = 15.12 volts max is 9.6 so 1.5 not good

2.5 is 30 x 17.39 x 18 / 1000 = 9.39 volts which is below the max 9.6 Wrong....max is 6.9V(including the VD of your final circuit) as you are feeding lights

So if i was to INSTALL this cable chosen 4mm rather than 2.5mm in the chance he wants more sockets or an auto garage door etc

4mm² would give you a VD of 5.77V on the distribution circuit which leaves you with 1.13V to play with on the final lighting circuit


4mm 3 Core NYY-J Cable Black
4mm 3 Core NYY-J Cable Black

4mm² armoured is cheaper
4.0mm 6943X 3 core SWA Steel Armoured Cable

That would be good enough to run from his mains-board inside out along a wall and wire into garage to a mainsboard?? from a 20A breaker (Upgrade to 32A breaker incase of upgrade)

Cheers

My Red & ​Green
 
One thing to remember though is there are minimum heights that over head cables need to be suspended at and maximum support intervals.

Tables D1 and D2 of Appendix D in the On-site Guide. Minimum height is 3.5m and the maximum support interval is 350mm
 

Reply to Teach me please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Solved
Please use the like button to thank, like or whatever. As the forum treats that as a positive message then and uses it to score members.
    • Optimistic
Replies
11
Views
1K
Hi, I hope you’re all well. To cut a long story short, I’m going to be a young Dad very soon and need some help/advice/peer review with an...
Replies
0
Views
318

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top