View the thread, titled "Temp factor .8 and 1.2" which is posted in Electrical Testing & PAT Testing Forum on Electricians Forums.

I have a new Metrel tester and it has a .8 factor to apply to ZS. for the temperature adjustment for the cable heating up from ambient as a result of a fault.

I see .8 mentioned a lot elsewhere, is this .8 a rule of thumb derived from the equations of : rT= R20 {1 + A 20 (0-20)} =1.2 (inverse of .8) ?

and

ZTest (Max) = 1 / f *Zs = 1/1.2 * ZS (where 1/1.2 = .83r) almost .8?

.8 as a multiplier to de-rate the tabulated value, and .8 as a divider to be applied to inflate the measured value?

Max tabulated ZS = 1.3ohm - derated to be compared with a measured value would become a (1.3*.8) = 1.04 max measured value, anything measured higher than 1.04 is too high.
If i have a measured value of ZS and i want to convert so i can compare it to a tabulated value: -
measured value = 1.04ohms /.8 = 1.3ohms - i can then directly compare the 1.3 to the given ZS of the relevant overload device?

Is that correct please?
I realise that the 1.2 is a factor that is dependent upon the type of cable, 70 or 90.

Thanks
John
 
Hi John,
This is my take on it. The values of Zs in BS7671 are taken at 70 Degs. C and those in On Site guide are at 10 Degs. C. Copper changes resistance by approx. 2% for every 5 degs. C . change Therefore difference between them is 60 Degs. (12 lots of 5 degs.) so from 10Degs. C to 70 Degs C is a 24% increase ( a multiplier of 1.24.) and the reciprocal of 1,24 (1/1.24) = 0.8. Therefeore multiplying the BS 7671 values by 0.8 will give an acceptable maximum Zs when measured. Otherwise use On Site Guide of GN3 for the values and one can make a direct comparison of measured values as these have already been multiplied by 0.8.
JohnC
 
Last edited:
as above.it's to allow for the increase in resistance of the cable. you measure at 20 dg.C, but the cable is rated to 70.C. very pessimistic, IMO as cables are rarely loaded that high as to ever reach70.C.
 

Reply to the thread, titled "Temp factor .8 and 1.2" which is posted in Electrical Testing & PAT Testing Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk

Thread Information

Title
Temp factor .8 and 1.2
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
factor

Advert

Thread statistics

Created
John-,
Last reply from
telectrix,
Replies
3
Views
2,536

Advert

Back
Top