I've been asked to supply a temporary cabin on a warehouse site.
The garage that services the trucks has a Square D D.B. (used as a Section Board) which feeds 3 other D.B.s in the garage, one 3 phase , one 110v and one single phase. All pulling no great load.
The supply to this sectin Board is from the Mains Shed where there is a Merlin Gerin S.B. and a 250 A MCCB which feeds the Garage Section Board via a 50 mm2 XPLE cable which is on rack ,tray and duct (duct for most of it's length)
The Zdb at the garage section board is 0.41 ohms !
I've used the cable mate site and and this does not comply as far as I can see.
There is no seperate earth conductor run with this XPLE SWA.
A large contractor installed this and I'd have expected it to be done correctly, or am I missing something?
From my understanding theMCCB is way oversized and will not meet disconnection times ( I think most prob as is was existing in the section board (premesis had a prior use ))
And the cable is undersized ( I get it at 90mm2)
There is no bonding directly at the garage Section Board but at one of the sub boards to gas,water and steel.
Therefore am I correct in saying I can not supply the temporary cabin from the Garage S.B. unless something is done about it's supply cable and/or MCCB ?
Many Thanks
The garage that services the trucks has a Square D D.B. (used as a Section Board) which feeds 3 other D.B.s in the garage, one 3 phase , one 110v and one single phase. All pulling no great load.
The supply to this sectin Board is from the Mains Shed where there is a Merlin Gerin S.B. and a 250 A MCCB which feeds the Garage Section Board via a 50 mm2 XPLE cable which is on rack ,tray and duct (duct for most of it's length)
The Zdb at the garage section board is 0.41 ohms !
I've used the cable mate site and and this does not comply as far as I can see.
There is no seperate earth conductor run with this XPLE SWA.
A large contractor installed this and I'd have expected it to be done correctly, or am I missing something?
From my understanding theMCCB is way oversized and will not meet disconnection times ( I think most prob as is was existing in the section board (premesis had a prior use ))
And the cable is undersized ( I get it at 90mm2)
There is no bonding directly at the garage Section Board but at one of the sub boards to gas,water and steel.
Therefore am I correct in saying I can not supply the temporary cabin from the Garage S.B. unless something is done about it's supply cable and/or MCCB ?
Many Thanks