I've been asked to supply a temporary cabin on a warehouse site.

The garage that services the trucks has a Square D D.B. (used as a Section Board) which feeds 3 other D.B.s in the garage, one 3 phase , one 110v and one single phase. All pulling no great load.

The supply to this sectin Board is from the Mains Shed where there is a Merlin Gerin S.B. and a 250 A MCCB which feeds the Garage Section Board via a 50 mm2 XPLE cable which is on rack ,tray and duct (duct for most of it's length)

The Zdb at the garage section board is 0.41 ohms !

I've used the cable mate site and and this does not comply as far as I can see.

There is no seperate earth conductor run with this XPLE SWA.

A large contractor installed this and I'd have expected it to be done correctly, or am I missing something?

From my understanding theMCCB is way oversized and will not meet disconnection times ( I think most prob as is was existing in the section board (premesis had a prior use ))

And the cable is undersized ( I get it at 90mm2)

There is no bonding directly at the garage Section Board but at one of the sub boards to gas,water and steel.

Therefore am I correct in saying I can not supply the temporary cabin from the Garage S.B. unless something is done about it's supply cable and/or MCCB ?

Many Thanks
 
Huddsy - Mains shed as in Mains room/boiler house etc. Its a stell building .

Lenny - Yeah i'ts turned down to 0.7 but thats still 175 A.

I spoke to NICEIC Tech today, explained the scenario, he took some figures off me and said it would be ok if it could be turned down to 50%... but it can't.

I found a Merlin Gerin 160 A MCCB on the premesis, I'll fit this although it needs a steel mounting plateas it is physically smaller.

I still say the cable is undersized though. We got the measuring wheel on it today and it's 140 m !

I cant get my calcs anywhere near it being acceptable using the cable mate program.

It was on of thebig outfits in the North East that installed it to.
 

Reply to Temporary cabin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
if the 3 spaces with charge points are always allocated to the same 3 flats, surely the easiest way is to run the supply to the load side of the...
Replies
9
Views
901
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top