Was at a small event recently providing generator power & distribution to the usual line-up of PA system, bar refrigeration, coffee stall, etc. plus a photographer's tent. The photographer had two budget Godox studio strobes.
I place a multimeter at the distro on AC voltage min/max and check periodically for early warning of any irregularities.
I understand this type of flash strobe works by discharging a voltage of circa 1,000V for a small fraction of a second, and would imagine a diode protects the supply from being back fed.
Each time the strobes were discharged, I was metering a momentary spike of circa 30V at the distro.
I've given power to photographers previously and never encountered this... my thinking is that one (or both) of these budget strobe units had poor/leaky diodes allowing the capacitor voltage to back feed.
Does anyone have any other thoughts as to the cause or similar experiences with this type of equipment?
The photographer was blissfully unaware and didn't really understand the problem - I told him if I metered >265V, that I'd disconnect, fortunately for him, it didn't - quite! The PA system circuit was feeding a power conditioner and the other circuits didn't support anything sensitive, hence setting 265V in my mind as the threshold I'd allow.
I place a multimeter at the distro on AC voltage min/max and check periodically for early warning of any irregularities.
I understand this type of flash strobe works by discharging a voltage of circa 1,000V for a small fraction of a second, and would imagine a diode protects the supply from being back fed.
Each time the strobes were discharged, I was metering a momentary spike of circa 30V at the distro.
I've given power to photographers previously and never encountered this... my thinking is that one (or both) of these budget strobe units had poor/leaky diodes allowing the capacitor voltage to back feed.
Does anyone have any other thoughts as to the cause or similar experiences with this type of equipment?
The photographer was blissfully unaware and didn't really understand the problem - I told him if I metered >265V, that I'd disconnect, fortunately for him, it didn't - quite! The PA system circuit was feeding a power conditioner and the other circuits didn't support anything sensitive, hence setting 265V in my mind as the threshold I'd allow.