I'm arranging to quote for a new build (my first new build). Ultimately will be PME. On plans, the supply head is to be rising in the centre of the property within a plant room.

How/where might you arrange the temporary (TT) supply for the site, when the slab and all the groundworks would be going on all around the final location of the head?
 
Thanks guys. I just spoke to DNO.
They say their procedure would be (on application).. Shorten existing supply (prior to demolition) to temporary location outside the property.
Cast-in a duct to the new head location (DNO has spec for the duct). After the build, the new supply is shoved up through the duct and old temp supply disconnected.
QED (it seems).

So thats the DNO's postion, what about the suppliers for the meter?
 
Most DNO's will insist that you have an outside meter box (OMB). Make sure if going inside the property, that you have it in writing from the DNO ie your application / drawing approved and signed by them. Is there gas (if any) going in same place?
Thanks, then I'll be getting that in writing off them since DNO verbally OK'ed my question on the phone. Customer doesn't want any external meter boxes.
 
Thanks, then I'll be getting that in writing off them since DNO verbally OK'ed my question on the phone. Customer doesn't want any external meter boxes.

Just out of interest really. when i worked for a DNO doing this type of work, customer had no choice unless it was Grade 2 listed or in a conservation area regarding the OMB. Many customers didn't want a OMB installing, especially at the front of the property. Hopefully your DNO do not have the same attitude.
 
Since when do they lay a building foundation slab on insulation?? Insulation will if anything be on top of the slab and under the floor screed.
Not anymore matey. The current trend is going towards putting your oversite/slab/whatever on TOP of your insulation, particularly if using underfloor heating as that way your mass becomes part of your thermal energy store.
 
Not anymore matey. The current trend is going towards putting your oversite/slab/whatever on TOP of your insulation, particularly if using underfloor heating as that way your mass becomes part of your thermal energy store.


LOL!! With the size of slabs i'm used to seeing, the insulation will end up the thickness of a smoke paper!! I'm just wondering how long that insulation will last too, especially in some of the corrosive soils i've seen over the years!!
 
Insulation is laid on top of dpm, on top of blinding.... Or often as well will be beam and block.
 

Reply to temporary supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
878
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
971

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top