gazroberts
Hi, I am new to this forum and wanting some advise on coding for a inspection and test on a industrial installation. I am a C&G qualified electrician with 17th and 2391 qualification. it is quite old installation around 1950's to date and hasn't been inspected before it has a mixture of lead sheath, v.i.r's conduits and s.w.a's. One questions is how many sub mains is acceptable, ie I have the 1600A main switch in the sub with a 200A switch feeding a 200A board, feeding a 100A board, feeding a 32A board feeding a 15Amp board (of which gas rings mains off it (with 30A fuse wire in a 15A fuse). is this breaking any regulation? I would only normal run 1 sub main from the original board. Should each submain have its own isolator / main switch, these are the Bill or MEM type 3036 rewirables that don't have built in main switches, if so what code. What code would you give a horizontal run of conduit with insufficient supports i.e every 3m between purlins. this also has extra weight of light fittings on it and is physically bowing. I have S.W.A's with unrecognised installation method for example zip tied to pipes or conduits or anything else for that mater, that's if they are tied to anything. what would I record if a circuit has two types of wiring for example a 3 phase circuit consisting of 4 single M.I.C.C's joined to a Lead sheath cable of different conductor sizes, or a 4core 4mm S.W.A joined to a singles 2.5mm conduit system. to be honest a lot of it needs ripping out just trying to back up my argument. Any help much appreciated. Gaz