I recently installed a length of SWA. When testing and certifying, do I simply use a domestic electrical installation certificate and test at the start of the cable (at main CU) with the sub CU isolator off? Would I need to do each circuit on the sub CU also, or just one set of tests for the actual cable?
 
Funnily enough I've done the same job today and I'm inclined to use a MWC to confirm the tests. Its only the "distribution" cable you've replaced so why go further?

Others may disagree, but an EIC for something so "straightforward" would be OTT.

You did replace the cable didn't you?
 
If you have replaced an existing cable because it was damaged etc, then a Minor Works is the right form to use. If you have installed the SWA as a new circuit, a distribution circuit, feeding the sub-board, then you need to complete an EIC for that circuit. Also if you have installed the new sub-board, you will need to complete a separate EIC for that board. Sorry, but your post did not give the full detail so that is the full story, choose whichever scenario applied. Regards,
 
I fitted the cable in place of an overhead supply. The sub board etc will stay the same as it was. Thanks guys
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Test certificate for new installation of SWA
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Diode,
Last reply from
Octopus,
Replies
6
Views
3,409

Advert

Back
Top