I'm making up a green test lead to use with my Megger 1553 with a plug adaptor for PFC and Zs tests.

I have bought 3A silicon cable, I need to know what sort of current the Megger generates for these test to see if the cable will take it?

Thanks.
 
Last edited:
I'm making up a green test lead to use with my Megger 1553 with a plug adaptor for PFC and Zs tests.

I have bought 3A silicon cable, I need to know what sort of current the Megger generates for these test to see if the cable will take it?

Thanks.
better off with 12AWG silicon cable...its about 2.5mm core and 4mm O/D will carry 30+amps will that...good for making up wander leads n all......
 
I'm making up a green test lead to use with my Megger 1553 with a plug adaptor for PFC and Zs tests.
I have bought 3A silicon cable, I need to know what sort of current the Megger generates for these test to see if the cable will take it? Thanks.


3A ?? Can you actually see the conductor?? What is the actual size of this conductor? Remember that multi stranded silicon cables have a higher current carrying rating than normal insulated cables....
 
I thought it would be a higher rating too!
It's 0.5mm2, OD is 2.6mm.
I bought a long length to use the rest of it as a wander lead. Which should be fine, as its low current!
I might just buy a different length for the PFC lead.

I worked it out on the adibiatic and it will take the 20A current for 0.008 seconds! Anyone know how long a PFC test lasts on a megGer
Thanks.
 
well with all due respect mate you said it.....so you think that because the PFC is only for a very short duration that alls good?.....over time and continued tensioning of this cable you plan to use it will just end up wilting on you...in time...and probably when you dont have a replacement and need it to do its stuff.....test leads are a certain CSA for a reason mate and dont forget the smaller the CSA...the higher the impedence......
 
Yes, I said it but didn't get the :p on the end to make it obvious it was a joke!
I appreciate that your saying. The resistance in the cable I bought is lower than my Megger test leads though. Also aren't you putting the same 20A through 1mm2 lighting circuits? And 5A rewireable fuses?
 
I use a Megger 1553. You can pretty much see the duration of the Zs test current if there are filament lamps in the house! Even when testing another circuit and you have a low Ze..
I'm going to take a stab at 40ms - 2 cycles.

Interestingly, there's one loading pulse on the high current test and two on the No-Trip test.
I know the blurb states 15mA for the no-trip test, but loading the circuit with 15mA wouldn't cause the short duration volt drops observed during the test.

Simon.
 
Last edited by a moderator:
Had a reply from Megger this morning:

Hello Mr **cock
Thank you for your email
As such the MFT1553 loop test does not generate a current to inject into a circuit. Basically the unit introduces a resistance across the supply and the volt drop is used to calculate the loop impedance. The max current that flows is approximately 18A. The CSA of the cable is 1mm
Regards,

I never believed how the AA batteries could manage 25A anyway, but as a few people I asked said it could, I went with that!

ringer: from RS Components,
This is the 3A cable I used for the wander lead (2x lengths)

This is the silicon 32A (overkill!) I used for a green test lead

There's a cheaper version, which is 19A PVC (I think thats what the shiny standard Megger leads are. I can't find it on the internet but its from page 1-75 onwards in the 2011 catalog.
 

Reply to Test lead current rating. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

Personally it would annoy me having to use adaptors all the time. Can't you buy a proper UK one?
Replies
6
Views
428
It's a room where someone sleeps, so it's a bedroom. Minimum standards were set in the Parker Morris report in around 1963. Anything built after...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top