dandanspark

Hello every 1 what is the easiest way\book to cross reference my test results, ie which book and page numbers Many thanks
 
for reference look in osg. there's not that many pages to look at. i'd look it up but i'm also lazy.
 
yes ZS readings, but basically all readings such as R1, R2 R1+R2, is there somewhere specific i can check my readings out to make sure they are all ok. i am pretty new to testing as you can tell. Thankyou
 
R1+R2 values can be calculated for any length of cable from table 9A. OSG. page 166.
max. Zs values are given in table 2D, page103. ( this is abbreviated just for MCBs, for fuses and fuller info., refer to the BRB.
 
Last edited:
As Tel said, R1+R2 readings will need to be calculated to verify cable length is ok.

Divide the R1+R2 result by the resistance/meter of the line and cpc of your cable from Table 9A. This will give you the length of the cable.

Maximum cable length for Zs can be worked out as below:


Radial
L = (Z[SUB]41 [/SUB]- Z[SUB]e[/SUB]) ÷ (mΩ/m x 1.2)

Ring
L = 4(Z[SUB]41[/SUB] - Z[SUB]e[/SUB]​) ÷ (mΩ/m x 1.2)

L = Maximum length of cable
Z[SUB]41[/SUB] = Max Zs value for the particular protective device from BS 7671
Z[SUB]e[/SUB] = External earth loop impedance
mΩ/m = Resistance per meter of the line and cpc conductors


However, maximum cable length is more likely to be limited by voltage drop. This can be worked out as follows:

Radial
L = (MaxVD x 1000) Ă· mV/A/m Ă· Ib

Ring
L = 4(MaxVD x 1000) Ă· mV/A/m Ă· Ib

L = Maximum length of cable
MaxVD = Maximum voltage drop (6.9V for lighting or 11.5V for power)
mV/A/m = Millivolts per amp per meter for the size of the cable from BS 7671
Ib = Design current of the circui
t
 

Reply to test referencing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

Because of the addition of separate columns for RCD type etc. I use Easycert software which gives the option of fitting it all onto one page.
Replies
1
Views
317
loz2754
L
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top