sima24
Hi guys,
Im currently training as an electrician and have been practicing my testimg at home. Was wondering if anyone can take a look at my results and see if they look "average" as its nagging me as i think it seems too low (zs too low)
Ring final figure of 8 test R1 + R2 = 0.31/4 = 0.07. Ze = 0.24 - zs = 0.31 ohms.
IR on the same circuit = 124 Mohms
Iv recorded pretty opposite results between downstairs and upstairs circuits
Upstairs lights IR = 116Mohms
Upstairs sockets IR = 124.7 Mohms
Downstairs lights = 6.38 Mohms
Downstairs sockets = 6.86 Mohms
Upstairs lights continuity 0.32 ohms
Downstairs lights continuity 1.38 ohms
Could anyone please shed any light on why these results differ so much? Im a bit confused as how to interpret these results, any help would be appreciated, thanks.
Im currently training as an electrician and have been practicing my testimg at home. Was wondering if anyone can take a look at my results and see if they look "average" as its nagging me as i think it seems too low (zs too low)
Ring final figure of 8 test R1 + R2 = 0.31/4 = 0.07. Ze = 0.24 - zs = 0.31 ohms.
IR on the same circuit = 124 Mohms
Iv recorded pretty opposite results between downstairs and upstairs circuits
Upstairs lights IR = 116Mohms
Upstairs sockets IR = 124.7 Mohms
Downstairs lights = 6.38 Mohms
Downstairs sockets = 6.86 Mohms
Upstairs lights continuity 0.32 ohms
Downstairs lights continuity 1.38 ohms
Could anyone please shed any light on why these results differ so much? Im a bit confused as how to interpret these results, any help would be appreciated, thanks.