tigerpaul

-
Arms
Joined
Nov 11, 2008
Messages
403
Reaction score
105
Location
Tadley
There are a few workshops where I'm based which have permanently hard wired 110v sockets fed off a fixed transformer. Its puzzling me how to obtain a loop impedance result on a centre tapped 110v system?
Any ideas?
I use a normal megger mft 1502.
 
I thought it is live - earth as with any loop impedance test. Your tester should test at 55 volts.

Obviously your maximum values are obtained from a different table, which I don't know off the top of my head.
 
I have done loop readings on 110 volt sockets, and thinking about it, it was with an MFT 1502. When you turn your tester to loop, it will display <55v I'm sure.

However, it is not possible to test RCD's on 110 volt systems as the MFT 1502, I believe, needs 110 volts or more.

I know that thereis no need for RCD protection on 110 volt systems, but the installation I was on had one for some reason.
 
The 1502 does start to measure at 55 volts. I would check my 1552 but it's in the garage with the batteries out and I can't be bothered... :lol:
 
Work gave me the 1502, I really miss the RCD auto-test function... :lol:

My employer also issues mostly 1502's, and has hundreds of them. I have not had the privilege of using the auto RCD yet, but I know some of the lads have had the 1552's or newer models. We get our testers swapped every 12 months for calibration.
 
I have done loop readings on 110 volt sockets, and thinking about it, it was with an MFT 1502. When you turn your tester to loop, it will display <55v I'm sure.

However, it is not possible to test RCD's on 110 volt systems as the MFT 1502, I believe, needs 110 volts or more.

I know that thereis no need for RCD protection on 110 volt systems, but the installation I was on had one for some reason.

Adam

If you cannot comply with table 41.6 which is for a reduced low voltage system (110V) then as per regulation 411.8.3 you can use an RCD for fault protection by automatic disconnection of the supply.

If by your post this is related
 
Your meter should have a settings menu where you can change between 240v, 60v, or 55v. On my Metrel you hold the screen brightness button whilst pressing any navigation key.
 

Reply to Testing 110v system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
265
That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
478

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top