Ross Trician

Afternoon all.

Can someone please tell me, when testing a 3 phase dis board for the Ze, PFC etc do you have to squarre route the reading or something, can't remeber what it is you do to it and can't find my testing book at mo, think i have lent it someone. ( can;t think who to and no doubt they wont return it)

thanx, Ross.
 
Afternoon all.

Can someone please tell me, when testing a 3 phase dis board for the Ze, PFC etc do you have to squarre route the reading or something, thanx, Ross.

Ze, same as a single phase board but you have 2 extra line conductors. Therefore you do each 1 individually and the higher 1 of the 3 is your Ze.

PFC, measure Pefc of the 3 individual lines to earth and the higher 1 is your Pefc.
Measure the 3 lines individually to N and the higher 1 is your single phase Pscfc. On a 3p DB the Pscfc between 2 lines will be higher than between 1 line and N. Some meters dont like 400v up 'em so this can be calculated by multiplying the highest L to N value by the sq root of 3. GN3 allows x2 as a rule of thumb which also errs on the side of caution.
The highest value is recorded as Pfc for the installation which will be the higher 1 between any 2 lines.
 
The highest value is the recorded one either it be L1/L2/L3 to E or L1/L2/L3 to N the highest is the recorded one you enter mate.
 
The highest value is the recorded one either it be L1/L2/L3 to E or L1/L2/L3 to N the highest is the recorded one you enter mate.

The highest level of PFC won't be any of the ones you've mentioned.
It will be between any 2 lines which can be calculated as I said above or measured if your meter is safe to do so.
 
You don,t measure the pfc between 2 lines my mate its the highest value whether it be L to E or L to N thats it


PFC will be higher as stated between the phases rather than between any phase to earth or any phase to neutral. You could measure via tha latter method, then use rule of thumb and multiply by Two.

Or even better, get a decent meter, Meggar 1550's are brill.

PEFC is the potential between any phase to earth, it is different to PFC, and has been covererd ....


:)
 
PFC will be higher as stated between the phases rather than between any phase to earth or any phase to neutral. You could measure via tha latter method, then use rule of thumb and multiply by Two.

Or even better, get a decent meter, Meggar 1550's are brill.

PEFC is the potential between any phase to earth, it is different to PFC, and has been covererd ....


:)

So the Megger 1550's actually can do the PFC between phases?

I was told they couldn't so have been using rule of thumb throughout:(
 
It's always worth checking your instructions to see whether your meter can cope with 400V. Unfortunately mine can't.

If in doubt, don't. Just test between each line and N - then double the highest reading it to get your approx reading for 3ph PSSC.

(I actually read in a Scadden book that really you should be multiplying by 1.732, but after querying with a tutor at college this is wrong and you should be doubling it. A mistake in a Scadden book - who'd have thought it ;) )
 
You don,t measure the pfc between 2 lines my mate its the highest value whether it be L to E or L to N thats it

Ok my mate Johnny you do it the way you see fit.
But if you get a short between any of the 2 lines the amount of current will be much higher than L-E or L-N. And the OCPD must be able to safely clear the highest possible amount of PFC.

(I actually read in a Scadden book that really you should be multiplying by 1.732, but after querying with a tutor at college this is wrong and you should be doubling it. A mistake in a Scadden book - who'd have thought it ;) )

Steve, I think Scadden is correct as the voltage between 2 Lines is 1.732 x greater than betwwen 1 Line to N:

VL = VP x 1.732

(1.732 is the sq root of 3 as I touched on in an earlier post. GN3 p52 allows 2x as a rule of thumb as it easier to remember and errs on the side of caution)
 
Last edited by a moderator:

Reply to testing 3 phase in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
602
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top