Can anybody help with this one?

Installation: TT system, (Ra 27 ohms), 3 phase & neutral incoming supply.

A 4 pole 30mA RCD is at the head of the board, from which there is a 3 phase motor circuit and a 3 phase & neutral feed to a second board. The second board has a number of 230V final circuits fed from each of the phases in turn.

When testing the RCD I get a figure of about 120mS at 30mA test current but at 150mA test current the test bombs out at >40mA. I can't actually configure the test set to record the operating time at 5 x Idn.

I changed the RCD for a new one and I get the same result.

I started off by testing this at one of the 230V final circuits. However, I get the same result if I test directly on the output terminals of the RCD - i.e. L1, N, CPC - ditto L2, L3.

I have checked the tester on a 2 pole 30mA RCD and I get the normal sort of operating times you would associate with a fully functioning device.

Any thoughts on the test method, or a configuration fault which might give longer than expected cut-off times?
 
Can anybody help with this one?

Installation: TT system, (Ra 27 ohms), 3 phase & neutral incoming supply.

A 4 pole 30mA RCD is at the head of the board, from which there is a 3 phase motor circuit and a 3 phase & neutral feed to a second board. The second board has a number of 230V final circuits fed from each of the phases in turn.

When testing the RCD I get a figure of about 120mS at 30mA test current but at 150mA test current the test bombs out at >40mA. I can't actually configure the test set to record the operating time at 5 x Idn.

I changed the RCD for a new one and I get the same result.

I started off by testing this at one of the 230V final circuits. However, I get the same result if I test directly on the output terminals of the RCD - i.e. L1, N, CPC - ditto L2, L3.

I have checked the tester on a 2 pole 30mA RCD and I get the normal sort of operating times you would associate with a fully functioning device.

Any thoughts on the test method, or a configuration fault which might give longer than expected cut-off times?


The above,may possibly be a clue,to what Lee has already mentioned :rolleyes2:
 

Reply to testing 4 pole RCD - funny results? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top