ambrad

Hi all

I am new to testing so need some advice.

I have installed a low voltage bathroom fan and would like to know do i have to test the whole lighting circuit it is attached to or just the the cable i have installed for the fan.

also should i bypass the transformer when testing to avoid incorrect readings. resistance etc.

thanks
 
Are you talking of an ELV fan? A 230v fan is LV.
I'd be tempted to carry out a full IR test on the cabling you've installed with all sensitive equipment disconnected then carry out an IR test of the whole circuit with L&N (connected together) to E.
 
If you look at the notes concerning the MEIWC on page 336 of the regs you will see the very last sentence states

​ Appropriate inspection and testing, however should always be carried out irrespective of the extent of the work undertaken"

Now only you will be able to deem whether and what is appropriate, and to test the existing installation or just the part you did. If the existing circuit has RCD protection and your just adding a fan then perhaps no, you would only test the part you did

If the existing installation is 60 yr old, has no RCD protection, which you will now have to give to that circuit and is VIR cable then yes I would definitely be testing it.
 
Last edited:

Reply to testing a low voltage bathroom fan in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There's not some fancy 'smart switch' with no neutral controlling the lights! 🤪?
Replies
5
Views
638
  • Question
Trickle +Boost would be the way to go if it's running continuously
Replies
3
Views
800

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top