Hi could someone help me please. I'm at college doing 2330 level 3. I'm currently doing inspection and testing. I need to know where I find my (r1+r2) on my sub main. Which is powering a double socket and a light. Thanks
 
can't be much of a sub-main then. is it in a shed or garage? to ger R1+R2, you would link L and E at the main DB, then measure at the sub incomer with the sub main switch off. think malcolm beat me to that by a mile, but i've been grafting, not on a cushy posting. LOL. :nopity:soz., malc. couldn't resist. beer's on me when you gey back to civilisation ( ahhh, just remembered, you live in kent. ). :dots:
 
Hi could someone help me please. I'm at college doing 2330 level 3. I'm currently doing inspection and testing. I need to know where I find my (r1+r2) on my sub main. Which is powering a double socket and a light. Thanks

Just for your info mate, as you are in training.

A sub main is exactly the same as any other radial circuit for the purposes of inspection and test, so the test methods are identical.

Where a sub main differs from a radial circuit, is in its application. A circuit which originates at a Consumer unit or similar and goes into the installation to supply lighting, sockets, cookers etc, is known as a radial circuit.

A circuit which originates at a Consumer unit or similar, and then goes to another consumer unit, like house to garage, then this is still wired as a radial circuit, but it is known as a Distribution Circuit (aka sub main).

The two need to be differentiated, because depending on certain things like protective devices, you can have disconnection times that are different on a distribution circuit from a radial circuit.

I will let you find the difference between a ring main, and a ring final circuit for yourself.

Cheers............Howard
 

Reply to testing a sub main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
285
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top