Hello everyone!
Has anyone been asked to test the main building incomers like ACBs as part of Periodic Inspection? If yes, do you give this part of the work to 3rd party? and what is the process and how you verify the report?
some of my bigger clients are asking for this test to be done.
Thanks in advance
 
I am pretty sure that ACB's should be serviced at intervals recommended by the manufacturer.
surely testing of them would be part of the service?
 
it would be best to clarify what the client means by testing.

ACBs should be racked out and various internal checks done periodically. Also at least once a year ACBs should be switched to exercise the springs. If there is a PLC this should also be confirmed as operational and all batteries and chargers conformed as in good order.

I would not entertain using any one other than a competent person to rack out an ACB and carry out the internal testing.

The switching and testing the PLC is something we do internally annually but we do have a level of competence to do this and a sound knowledge of the system it is not the competence required to rack out and test internally an ACB.
 
it would be best to clarify what the client means by testing.

ACBs should be racked out and various internal checks done periodically. Also at least once a year ACBs should be switched to exercise the springs. If there is a PLC this should also be confirmed as operational and all batteries and chargers conformed as in good order.

I would not entertain using any one other than a competent person to rack out an ACB and carry out the internal testing.

The switching and testing the PLC is something we do internally annually but we do have a level of competence to do this and a sound knowledge of the system it is not the competence required to rack out and test internally an ACB.
I guess they want to make sure the springs would work properly and disconnects the load if they want to manually switch it off . also in case of a fault, it trips safely. which if I am not wrong, means all the procedure that you have mentioned shall be done and it is better to be done by a specialized company not part of general fixed wiring tests
 
The ones I've seen tested were;

Mainly 2000amp, but size won't have too much effect on the costs.
Tested by a specialist
Required isolation of the (11kv) incomer by the DNO
Consisted of inspection / torque check of terminations.
Verification of settings to suit site
General condition check
Simulated load test using a test rig and a built in test facility.

Replacement with spare if faulty or failed test.

This was a new program set up after a series of ACB failures.
The failure wasn't to trip it was failure to reset due to springs / levers jamming in the open position.

As per ESSEX, they should be operated routinely.
 
The ones I've seen tested were;

Mainly 2000amp, but size won't have too much effect on the costs.
Tested by a specialist
Required isolation of the (11kv) incomer by the DNO
Consisted of inspection / torque check of terminations.
Verification of settings to suit site
General condition check
Simulated load test using a test rig and a built in test facility.

Replacement with spare if faulty or failed test.

This was a new program set up after a series of ACB failures.
The failure wasn't to trip it was failure to reset due to springs / levers jamming in the open position.

As per ESSEX, they should be operated routinely.

Hi Snowhead Why did the HV need isolating to test the ACB ?
 
Hi Snowhead Why did the HV need isolating to test the ACB ?

Often the acb is directly connected to the transformer.
In that case,
That is the only way to isolate it.
 
I guess they want to make sure the springs would work properly and disconnects the load if they want to manually switch it off . also in case of a fault, it trips safely. which if I am not wrong, means all the procedure that you have mentioned shall be done and it is better to be done by a specialized company not part of general fixed wiring tests
They also probably put a full load on it to make sure it trips
 

Reply to Testing ACBs during Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
611
  • Question
The rent deposit schemes are very "Pro" tenant . And tend to always believe a tenant more than a landlord . With smart phones been almost a common...
2
Replies
29
Views
3K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top