V

volta1

a 10amp type c has a max measured zs of 1.85,i have a circuit with a measured zs of 2.03 the circuit is 2.5mm (not sure type) and it provides roof lighting also r1+r2 was 2.77ohms. is there any way i can make the zs result acceptable using the design zs from the regs or does this circuit just fail? i could reduce the mcb to a 6amp but dont want to.
 
there are a few ways to do it 1st check all connections ensure they are tight , high R1 + R2 and Zs could be due to loose connections , also depends on the length of cable run , the other way is to increase the size of the cpc ,and the other option is to install an RCD . first i would have a rough idea on the cable length if for instance the lenght of the cable is 30 meters then you R1+ R2 reading should be around the 0.59 ohms up to about 50 meters it should be around 0.98 ohms so if you work on those values it may give you an idea of what your readings should be but i place my money on a loose connection some where.

details of R1 + R2 values are on table 10.1 of the on site guide :rolleyes:
 
Last edited by a moderator:
I would check the circuit first, see if you have any loose conections things like that.

Instead of that C type have you thought of using a B if there are not large in rush currents.

If the circuit is wired in singles you could rewire with a larger CPC.

You can also use supplementary bonding to help with the Zs.

The 2.77 ohms does seem high to me, it is either a massive run, and the 2,5mm^ is undersized. My gut instinct here is there is a loose connection somewhere.
 
this is someone else's test sheet that they have deemed acceptable,ive tried to make it acceptable using gn3 but can't,was wondering if can be.or if it just fails as it stands.
 
It fails as it stands as the Zs exceeds the permited value , we can,t suggest any more than malcome and my self have suggested , there could be an under lying problem ie loose connection as we both have mentioned or iits a masive cable run , the only way to sort it out is to carry out investigations , and would have been what id have put down on a periodic inspection observations sheet : Measureed Zs exceeds permitted limits requires further investigation and it would have been given a code 3 ,requires further investigation
 
Last edited by a moderator:
As the others say the circuit needs checking for a loose connection, if it is a loose connection in time it will get worse so it is best by far to find what sounds like a faulty connection.
Paul
 
this test result has been deemed acceptable by a super intelligent engineer.who has used his superior knowledge to calculate the result and deem acceptable using the design maximum zs(2.30)off the top of my head.just want to know if this is possible.lets assume the circuit is very long and there are no loose connections.
 
The maximum Zs to table 41.3 for a 10amp type C BS 60898 is 2.30 and you have used the rule of thumb to bring that down to 1.84.

Now you have said that they measured the Zs, I assume a live test and it was 2.03 and we can assume that is becasue of all those lovely parallel paths, that is because your R1+R2 was 2.77 and so the Zs is a lot lower than the equation would be.

Now to design this you will need the equation Zs = Ze + (R1+R2) so what do we know

Ze ??
R1+ R2 = 2.77 Do you know the Ze value or more to the point did your engineer

Another design way to find R1+R2 is Mohm/m X length/1000 so do you know the length of the run? or more to the point does your engineer.
 
this test result has been deemed acceptable by a super intelligent engineer.who has used his superior knowledge to calculate the result and deem acceptable using the design maximum zs(2.30)off the top of my head.just want to know if this is possible.lets assume the circuit is very long and there are no loose connections.

Manufactures info will differ from the brb, so some leeway possible there.
 
this test result has been deemed acceptable by a super intelligent engineer.who has used his superior knowledge to calculate the result and deem acceptable using the design maximum zs(2.30)off the top of my head.just want to know if this is possible.lets assume the circuit is very long and there are no loose connections.

Stick a fuse in down stream, make the mcb a distribution circuit, then the fuse the final circuit
 
Hold on before we go rewiring the installation let's see if we can find out if there is a problem. Sticking it on a RCBO will overcome all the problems but that is not avoiding the fact that he as a circuit design that is not meeting it's disconnection time.

I don't know if this is a EIC or a PIR as the OP just tells us it a cert, but let's make sure we don't have a problem with the circuit
 
I don't know if this is a EIC or a PIR as the OP just tells us it a cert, but let's make sure we don't have a problem with the circuit



this test result has been deemed acceptable by a super intelligent engineer.who has used his superior knowledge to calculate the result and deem acceptable using the design maximum zs(2.30)off the top of my head.just want to know if this is possible.lets assume the circuit is very long and there are no loose connections.





Hold on before we go rewiring the installation let's see if we can find out if there is a problem. Sticking it on a RCBO will overcome all the problems but that is not avoiding the fact that he as a circuit design that is not meeting it's disconnection time.

Thats another way, maybe there is an rcd of some descript upstream of the mcb?
 
Last edited:

Reply to testing calc question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
251
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
684

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top