D

dochisholm

hi eveyone i have recently gone out on my own and have performed my first periodic inspection which i want to get get spot on i have come accross the following queries which i am strugling to solve. the con unit has a huge opening at the top which i would say doesnt meet ip ratings as i can get my hand in would others suggest a board change or some sort of cover strip installed. The cooker is fed from a single socket on the ring no accessible isolation above worktop what code would people put. Finalyy limitations i have done end of line on lighting circuits and checked 10% switches visualy would this need to be put in limitations or is that a given as it is stated in gn3. every socket has been checked for polarity and loop. There is no main earth conducter i believe the supply to be a tt system max zs allowed to be recorded as all circuits are protected by 30ma rcd would it be same for every circuit despite mcb size rating thank you
 
the hole on the board is a code 1.
is the cooker plug/socket accessible for isolation? if so, no code needed.or poss. a code4.
you should check all switches visually ( presence and connection of cpc) . R1+R2 measured at each light with switches on, lamps out.
every socket off, visual and R1+R2.
r1,r2,rN for end to end of ring finals
main earthing conductor missing, code1. ( how can you measure Zs and Ze?)
you can't "believe" it's TT, you have to find out what if anything it is and rectify it.

there's more, no doubt somebody else will add.
 
This guide may help:
http://www.select.org.uk/downloads/Periodic%20inspection%20reporting%20-%20recommendation%20codes%20for%20domestic%20and%20similar%20electrical%20installations.pdf
I would say that if the hole at the top is that big it would be a code 1. No accessable Isolation Code 2.
I always list % of fittings inspected in the limitations- believe this is good practice
I am more concerned at the absense of a final earth conductor, even a TT system has this if you cannot find it or the rod it may be relying on the water/gas bond for an earth - you need to be sure on this or list it as a code 1.
 
On a TT system you should still have an earthing conductor, it should be connected to an earth electrode.

The IP code is 4X for the top surface of a distribution board.

What is the rating of the cooker? Some are designed to plug into a 13A socket.

Guidance Note 3 does not SPECIFY inspection percentages so you must list yours in the 'agreed limitations' box.

Max Zs allowed would be 1667 Ohms on every circuit if 30mA rcd protected.

Remember your electrode resistance should be below 200 Ohms for stability.

You must have an above-average knowledge of BS7671:2008 to carry out Periodic Inspection Reports, get Guidance Note 3 too and feast on it!
 
Just remember as well, that you are there just to test and inspect, not mend unless you have agreed this. Think of it as a bit like taking your car for the MOT, you pay, pass or fail. And then get charged for any work carried out, no matter how dangerous the car maybe they cant stop you driving it away, just like we cant turn off their electric.

You could ask about PIR codes till you are blue in the teeth, and you will get varying answers depending on how different people interpret the problem. Its down to you as the Testing electrician on the job to assess the condition and code as appropriate. This is where IQ Electrical's very good post kicks in, its all about knowing BS7671, and GN3. It will come with experience, keep plugging away, even with experience I probably don't always get it right.

Cheers........Howard
 
hi thanks everyone and i feel i do have a good grasp of gs3 which i have however i am far from able to recite it. Firstly the board would it be acceptable as the hole is manafacture moulded not just smashed to cover it with some sort of strip to increase the rating and save a board change as its not that old. The single socket on the ring is only accesible if the cooker is slid out i cannot see what code to apply to this a regs ref would be usefull if anyone knows. Telectrix in gs3 it states it is not possible to inspect every joint and termination in which case a sample inspection should be made is this incorrect as checking every switch and every socket would take an age on an inspection. It also states that a earth loop should be done at the end of radial circuits so i take that as not all is this the same for R1+R2 I know the missing earth conductoe missing is a code 1 the rod is present however whoever did the last board change didn't connect it to the board. I said believe as the old textile insulated cable goes into a non accesible singlepahse header and i couldnt accertain if it was an old pme or a tt. The cooker is designed to plug in however its the non accesible isolation which im unsure about. sorry this is a bit mixed tried to address each point as i read down
 
Both BRB (appendix 6) and GN3 (chapter 5) mate.

And I don't think the PIR forms are just for domestic.

The model forms in BS7671 2008 don't make any distinction between domestic and commercial however the scheme providers all have their own 'Domestic Periodic Inspection Report' form.
 

Reply to testing codes and queries in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top