M

mikeeb12000

HI
Does anyone know how i would go about testing for earth continuity on a school.
There is some pipework close to the main DB but i cant find the earthing conductors at the main gas & water and its miles from DB.
Thanks
Mike
 
External Earth Continuity or Ze is normally done at the first accessable point on the installation. this is usuallt at the main D,B as Supply authoritys fuses ar sealed. Isolate the whole installation and disconnect the main Earthing conductor. Clamop on to the Conductor and Test Ze and PFC. Remeber to reconnect con

Dont worry about your MAin Bonding Conducter at the moment thay are tested using the long lead method which should have been your first test you did.
 
Do you mean Main Earth Bonding continuity? If so, find the main Stop Valves for water and Gas supplies and there should be an earth conductor within 600mm of the consumers side of these.
If not you may have found yourself another job.
 
Last edited by a moderator:

Reply to Testing Earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
658
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top