doglog

Hello, can anyone give me some help on testing. I need to do an Insulation Resistance test on a lighting circuit with 24 ELV downlighters on it with individual transformers. I can do the live/earth and neutral/earth by testing live and neutral together to earth but the live/neutral test always gives a reading (obviously) even with the lamps removed (again obviously). I know if there was a live/neutral fault the breaker wouldnt set but is there some way to carry out this live/neutral test without disconnecting all the transformers.
Thanks for your help
Paul
 
but that doesnt PROVE Insulation Resistance is all clear between live and neutral does it..if there was a live/neutral fault I would only find out when energising and BANG..??:eek:
 
lives to earth is all you need for periodic but if its a new instalation L-N should have been tested befor the connection of transformers
 
Sorry Paul for not offering a solution that doesn`t involve disconnecting the tx, but there`s not one that i can think of.

Assuming this is indeed a new install, you should have first tested all LV conductors upto the disconnected Selv transformers @ 500v, then between individual secondary conductors on the ELV side @ 250v.
Finally, tested between live conductors (connected together) of Selv secondary circuit and those of the LV primary side & any other adjacent LV ccts. This should be done @ 500v.

A bummer i know, but there it is m8
 
Last edited by a moderator:
Thanks for your help.the installation is indeed new and it was 2nd fixed before I could get to test it..also all the lights have been calked around and decorated so Id better not disturb them to disconnect transformers..
I will test both live and neutral to earth and assume live/neutral to be clear if breaker sets ok..
Many thanks guys;)
 
Should always do I/R tests before installing l/v s , We always use Wago 3 lever connectors just in case we need to retest. :D
 

Reply to testing elv downlights in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top