Hi All, When testing exposed metal work to establish whether it needs bonding you: You test from main earth disconnected from MET to exposed metal work insulation tester @ 500V what readings should you expect if it needs bonding ? Also when testing with a continuity test what readings should you expect then ?
 
The formula is:
Rcp>(Uo/Ib)-Ztl
where:
Rcp is the measured resistance between the conductive part concerned and the MET of the installation (in ohms),Uo is the nominal voltage to Earth of the installation (in volts), Ib is the value of current through the human body (or livestock) which should not be exceeded (in amperes), and Ztl is the impedance of the human body or livestock (in ohms).


Rcp>(Uo/Ib)–Ztl=(230/0.01)-1000=23000–1000=22Kohms
 
Supplementary Bonding. (22Kohms) You cannot use a low resistance ohm meter. Insulation resistance tester on pipework & a known earth: above the value of 0.02Mohms, just a piece of metal. Below the value of 0.02Mohms, extraneous conductive part this should be bonded.

The calculation in sintra post above, relates to 10ma as a maximum amount of current in that location to pass through the body.

Hope this helps
 
Last edited:
The formula is:
Rcp>(Uo/Ib)-Ztl
where:
Rcp is the measured resistance between the conductive part concerned and the MET of the installation (in ohms),Uo is the nominal voltage to Earth of the installation (in volts), Ib is the value of current through the human body (or livestock) which should not be exceeded (in amperes), and Ztl is the impedance of the human body or livestock (in ohms).


Rcp>(Uo/Ib)–Ztl=(230/0.01)-1000=23000–1000=22Kohms

Or as I do it:

(230/0.005) - 1000 = 45kohms as I was always taught that the max current allowable through the body (Ib) should not exceed 5mA when determining whether or not something is extraneous.

p.s. I'm not saying you're wrong :)
 
Or as I do it:

(230/0.005) - 1000 = 45kohms as I was always taught that the max current allowable through the body (Ib) should not exceed 5mA when determining whether or not something is extraneous.

p.s. I'm not saying you're wrong :)

And here we are full-circle...
10mA is classed as the "let-go threshold", and used to be (not sure if it still is) the rating of RCD's in hospitals. I agree 5mA is much safer as a limit, but 10mA is generally accepted as safe, for the use of calculations.
 
Haha, full circle indeed! Yes I agree, 10mA is widely regarded as the figure to use, I just personally choose to use 5mA on the back of several recommendations official and unofficial and also because like you say, it is a safer figure to use.

I wouldn't be classing an electrician as incompetent if they chose to use the figure of 10mA, although I would always push to have them use 5mA instead :)
 
Guide to effects of current on human beings and livestock provides data for Ztl and Ib. For hand-to-hand contact, the value of the body impedance is given as 1000 Ohms in dry conditions where Uo is 230 V. You can then select a value of Ib between the two extremes:0.5 mA – the threshold of perception and 10 mA – the let-go threshold.
 
OP, you are testing whether the pipe is extraneous (i.e. already effectively already at Earth(ish) potential)...with that in mind you leave the Earth connected at the MET when testing with an Insulation Resistance tester - you are comparing "the lump of metal in question" with a known Earth potential.
 
Apologies if I am missing the blindingly obvious here but why do you need to disconnect the main bonds to do the tests?

Are we not looking for exposed metalwork which requires bonding after main bonding has been applied? There is surely a possibilty that you will find a bunch of exposed pipes which are continuous metal from the incoming supply that will be identified by this test as needing supplementary bonding despite the fact that these pipes will be effectively bonded when the main bonding is re-connected. You coukd end up adding extra bonding unecessarily.

What is supplementary bonding actually supplementary to? I was under the impression that it is a bond intended to supplement the main bonds? ie: a bond which is applied after the main bonding to supplement it where needed.
 
OP, you are testing whether the pipe is extraneous (i.e. already effectively already at Earth(ish) potential)...with that in mind you leave the Earth connected at the MET when testing with an Insulation Resistance tester - you are comparing "the lump of metal in question" with a known Earth potential.

You don't have to leave it connected to the MET. In fact, I usually find it easier to disconnect the main earth cable from the MET, rather than taking everything else out.
 
I am not sure if the original question relates to main or supplementary bonding and I think some posts are referring to one and some to the other.

Apologies if I am missing the blindingly obvious here but why do you need to disconnect the main bonds to do the tests?

For main bonding - to determine if a part is extraneous in itself, obviously any connections it may have to the met and other extraneous parts should be removed.

For supplementary - all main bonding and cpcs will be left connected.



Are we not looking for exposed metalwork which requires bonding after main bonding has been applied? There is surely a possibilty that you will find a bunch of exposed pipes which are continuous metal from the incoming supply that will be identified by this test as needing supplementary bonding despite the fact that these pipes will be effectively bonded when the main bonding is re-connected. You coukd end up adding extra bonding unecessarily.

What is supplementary bonding actually supplementary to? I was under the impression that it is a bond intended to supplement the main bonds? ie: a bond which is applied after the main bonding to supplement it where needed.
Yes.
 

Reply to Testing exposed pipe work in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
516
loz2754
L
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
161
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
487
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Replies
24
Views
1K
  • Article
This is an RSS feed of thread: Hole in copper pipe, solder under floor, T coupling & protection Content of the thread: I was stupid enough not to...
Replies
0
Views
117

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks