Hi guys I have my assesment in little over a month, and looking for some advice when testing my log cabin.
Do I need to fill out 2 test sheets. As my log cabin has it's own TT system. How would I measure Zs at my cabin? Im aware I Would only have Ze at origin DB.
Sorry been out the game a while and I'm aware I need to really brush up on my testing. Thanks
 
Ok. Topic been discussed before on here, and will no doubt be talked about again. I think the consensus on here, is to use the earth supplied by PME system, unless that's something declined by DNO, extraneous pipework in shed/log cabin etc causing issue with bonding or its a hot tub etc. You should just have your rational for your assessment, as you might be asked. There is a download, on supplies to remote buildings, in the resources section, which discuss the options.

As regards testing, your Ze is at your origin (e.g. house CU), unless it has its own distribution circuit, and Zdb at the log cabin CU.
 
You have a new distribution circuit from the house supply.
Inspect, Measure and test that seperately.
Then you have a separate installation in the shed with an incoming supply from the distribution circuit and outgoing final circuits all RCD protected.
Inspect and test that as a separate item.
If I were filling out the paperwork I would list the distribution circuit as the first item on the schedule of test results and indicate that it was part of the house supply only.
However if I were doing it for an inspection then I would have two EICs, one for each section.
 
I agree with Richard, if you have a new distribution circuit then the new installation in the log cabin it maybe clearer to an assessor if you produce separate Certs due to the different earthing systems. Which ever way you do it as one Cert or two ensure it is clear especially if you opt for one.
 
My property has a PME system. I opted for this because I didnt want any problems to conflict with my main DB and be isolated to log cabin.

How does this isolate problems to the log cabin? Unless you’ve installed an isolating transformer in the supply to the log cabin I don’t see how you’ve isolated anything to the log cabin?

If you’ve designed the installation well then the protective devices in the log cabin will operate on any fault in there without affecting the main DB.

What is the Ra of the earth electrode you’ve installed?
 
Why do I think the OP is unlikely to reply anymore. I do wonder sometimes chaps, if you look at your replies, why anyone is prepared to put their heads above the parapet and ask anything on this forum these days.

Perhaps we all need to get in touch with our feminine sides, present company accepted Sparkychick :)
 

Reply to Testing garage CU for assesment!!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
530
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top