Hi guys starting a new job testing commercial properties, i have passed my 2391 a few years ago and im just looking to refresh myself<

1: when doing an IR test on circuits protected by rcbo's to i have to disconnect both neutral and earth flying leads?
2: what are the flying leads on rcbo's actually for
3: when carrying out a Z's on a socket ring does everything have to be unplugged from sockets
4: same as number 3: for continuity tests


Many Thanks
 
1, Yes disconnect everything, but the cpc's must remain connected to the main earthing terminal whilst the circuit is under test.
2, The cream one is a functional earth, it wont work without it connected, the neutral is to enable connection to the neutral bar.
3, No
4, No, but i would disconnect to ensure no faulty loads give dodgy readings.

I would get GN3 and refresh yourself, it will all come back to you in a flash.

Cheers...........Howard
 
Hi guys starting a new job testing commercial properties, i have passed my 2391 a few years ago and im just looking to refresh myself<

1: when doing an IR test on circuits protected by rcbo's to i have to disconnect both neutral and earth flying leads?

I leave the neutral and earth flying leads in place and disconnect the circuit line and neutral from the RCBO. As above, leave the CPC connected to the earth bar.
 
1, Yes disconnect everything, but the cpc's must remain connected to the main earthing terminal whilst the circuit is under test.
2, The cream one is a functional earth, it wont work without it connected, the neutral is to enable connection to the neutral bar.
3, No
4, No, but i would disconnect to ensure no faulty loads give dodgy readings.

I would get GN3 and refresh yourself, it will all come back to you in a flash.

Cheers...........Howard

On the 'functional earth' point, what do they actually do? they test perfectlt without them
 

Reply to Testing Help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
376
  • Question
well then, must be a fault on the circuit, a faulty appliance if a power circuit or a faulty RCBO.
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top