J

jamminuk

Hi,

Just wondering how you would test IR when there is serge protection in the installation? Would it be a case of linking it out or reducing the test voltage?

Also why would a test for Zs trip RCD? :banghead:

Thanks again in advance

Ben
 
Hi,

Just wondering how you would test IR when there is serge protection in the installation? Would it be a case of linking it out or reducing the test voltage?

Also why would a test for Zs trip RCD? :banghead:

Thanks again in advance

Ben

You can test at 250V dc but the result must still be greater than 1MOhm.

The voltage is reduced to prevent the SPD from leaking to earth (as it should) at higher voltages.

As for the Zs test, think about the current that the tester is applying between L and E on an earth loop impedance test. ;)
 
Between which conductors?
Thanks.

Generally, you'd be able to test between all conductors at 250V dc but you'd still be subjected to the same constraints from other sensitive devices (ballasts etc.) that might mean you'd be testing with L+N combined to Earth.
 

Reply to Testing IR with serge protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
592
loz2754
L
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top