H
hughesy124
testing a mcc panel to day took ze at panel got 0.16 .then went to first mcb a 6amp c rated .zs was 10.56 which is very hi. did all checks to see if it was a bad earth . all looked to be ok .did r1/r2 reading which are ok .would hi zs reading be from mcc control gear .how can i get the right reading for test sheets.all help welcome many thanks .ps this is my first time on this site.
If the circuit was a motor through a DOL starter this is quite possible, especially if the overload is of a low range. We have stopped fitting overloads under 1 amp. Remember on a single phase over load the live goes through the overload twice and the neutral also goes through the overload and there is also quite a high resistance through the mcb. This is why HRC fuses are common in MCC panels.
need help
When you say a MCC panel, are we talking of 2 or 3 drive or dozens. I ask because it would change how I would earth a panel. The 2[SUP]nd[/SUP] question is where are you taking your readings from?
hi it;s a boiler house control panel .The reading is coming from top of dhw pump isolator with the switch off . looking to get Zs reading to fill in test sheet . looks to be a Trent system .also switch all other off to see if that would help but still the same very hi about 10.56 ohms ..check all other in boiler house and all are coming back the same.
If you got time and really wanna find the root cause of this high Zs I would take a Zs at the mcc panel where the outgoing circuit leaves and connect your testers earth to the outgoing conduit/trunking/swa so your testing the outgoing circuits earth path and not direct to the panels earth bar.
Go to each point and get a Zs untill you find the cause. remember to test the in and out side of switches.
An R2 test would let you know if your cpc condition so if that was low the high Zs may be due to control equipment or a fault switch. Is the trunking earthed? is there a seperate cpc of is it main frame, and corrosion?
Had exactly the same results when testing at isolators,supplies going thru o/l of contactors, all other tests R1 + R2 were fine.Reported to gaffe,still dont know the outcome ta ra bab
Reply to testing mcc boiler house control panel . in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...