Hi Again Guys,

I've just wired a garage unit and have fed It from a 32A MCB from the main cu in the house, so its a new circuit. I have tested the new unit and all is fine. The question I have is.. Do I have to test all circuits in the original cu as well and record results on the same test schedule as the garage one?

There are no records/certs/charts for the original cu.

Thank you all in advance
 
You just need to test and record the new circuit you have put in Bob, and then complete an EICR.

Also, because you have created a new circuit the work will be notifiable, so this may be a good job to show your assesser if you are not already part of a scheme.

Also you would need to make sure the Main earthing and Main bonding are acceptable.

........

I think we all typed at the same time!!
 
One tip for you when filling out the EIC for the "existing" CU, where the CU has existing circuits put "used" against these circuits, fill out the full details for your new circuit, and use "spare" for any remaining circuits.

Then on the sheet for your new CU in the garage fill out the cert for your new circuits, then "spare" for any unused.

Hope this helps.
 
One tip for you when filling out the EIC for the "existing" CU, where the CU has existing circuits put "used" against these circuits, fill out the full details for your new circuit, and use "spare" for any remaining circuits.

Then on the sheet for your new CU in the garage fill out the cert for your new circuits, then "spare" for any unused.

Hope this helps.


the old cu has no ID on any of the circuits so I can just write used where circuit description is? other wise I need spend some time finding out whats what. the old unit was fitted by the kitchen fitter. it has one rcd protecting 2x 32a circuits and all other circuits unprotected. its a chint board
 
the old cu has no ID on any of the circuits so I can just write used where circuit description is? other wise I need spend some time finding out whats what. the old unit was fitted by the kitchen fitter. it has one rcd protecting 2x 32a circuits and all other circuits unprotected. its a chint board

Yes.

As for the Chint - is that a spelling mistake as I think they are shint!
 

Reply to testing new and old db in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You'd have to be mindful of SPD conductor lengths doing it that way. I think Matt:E make a single board with Type A RCBO, openPEN detection and...
Replies
1
Views
1K
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top