ive just completed a new installation,,, all ok... except one lighting circuit... an insulation test phase to eth...400+ M/ohms .ok..but there seems to be
a low reistance from n to eth....? 0.79 ohms. theres two way/intermediate & several downlighters....ensuite fans/isolaters.etc...
pulling my not so thick hair out!!!...cpc continuity ok through to end of cct.and all works ok. need experienced advice.regards.andyp
 
If your reading is in ohms then you have a near short in some wiring; if it is in Mohms then I would be looking for items with circuit boards in them such as the fans, if you have isolators everywhere then test the circuit with these isolators off (assuming they are double pole) and this should narrow down where to look for the problem.
 
From my experience, the only way you would have got 0.79 Ohms while doing an IR test is if you had switched your instrument range to read continuity.

If you are measuring N-E, then you have either got a dodgy piece of electronics connected or crossed your neutral and cpc somewhere, assuming its not an TN industrial board.
 

Reply to testing new lighting cct in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
962

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top