A friend of mine had a refirb, extension and new rewire done back in 2007 before i was registered with the NICEIC. He has never had it tested or passed by building control and because it is coming up to the end of the time to sign off he has asked me if i can test the installation and issue a cert. Is it ok to fill out the 17th edition Electrical installation forms for this or should i just do it on a periodic report
 
Its far too late for an EIC, it will have to a PIR to the 17th edition regs which probably means there are going to be a lot of code 4 defects
 
Not sure from your post whether you carried out the work or someone else did,but doing an electrical installation cert on work carried out by others is a definate no-no anyway.
 
If you carried out the work then I don't see the problem. But it must be stated that it was designed and constructed in line with the 16th edition...
 
I agree with Trebor do a PIR its to late for an EIC now and your agreement with NICEIC is all work to 17th edition. If you do an EIC to 16th your in breach of your agreement and putting your hands up to building control for failing to notify. PIR saves all the possible grief.

Hope that helps


Chris
 
hi all

if a pir is carried out on the installation you wont be able to notify as you cant part p a pir... maybe you could upgrade to 17th and then issue a eic .:)
 
I have just done what Gary suggested, finished off several circuits from an incomplete 16th edition rewire, then converted the whole lot to 17th edition, every circuit was legitametly modified to such an extent I was able to issue a EIC.

However as also stated, if you were involved in the initial rewire then buy a split load/17th kit and convert it and issue your certs!
 
what would you guys do, lets just say for arguments sake, if someone 'ahem' rewired their own house before they were nic registered and before the cable colours changed and had a 16th edition board, never put a cert on it cause said person wasn't registered at the time, but were registered now and was to say put a 17th edition board up 'over' the old colours cause they were moving soon and needed an eic. said person was 100% confident their instal would meet 17th criteria apart from old colours. would anyone put a cert on their own house? just out of interest, theoretically speaking, just wondering? not that i know anyone who's done it! :rolleyes:
 
what would you guys do, lets just say for arguments sake, if someone 'ahem' rewired their own house before they were nic registered and before the cable colours changed and had a 16th edition board, never put a cert on it cause said person wasn't registered at the time, but were registered now and was to say put a 17th edition board up 'over' the old colours cause they were moving soon and needed an eic. said person was 100% confident their instal would meet 17th criteria apart from old colours. would anyone put a cert on their own house? just out of interest, theoretically speaking, just wondering? not that i know anyone who's done it! :rolleyes:

If your putting a 17th edition board in why don't you just do an EIC for that and leave it be.
 
Have just done that exact thing on my house. Did a total house refirb on my own house that my partner owns and we both live. NICEIC assessor said it was fine to do that
 

Reply to Testing old 16th edition installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

Similar threads

You are allowed a sampling process, i feel it would be impossible to I&T every point. If the client is prepared to pay for that so be, you can use...
Replies
8
Views
2K
Concerning isn't it. I fear it's just going to lead to reduction in standards and entry requirements and flood the industry with even more poor...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top