Testing RFC in earthed steel conduit... | on ElectriciansForums
Discuss Testing RFC in earthed steel conduit... in the UK Electrical Forum area at ElectriciansForums.net
DNS1
Excuse my ignorance on this, never had to test a RFC when the conduit was being used as the CPC.
Obviously can't do the usual test for continuity so can't tick that box on the form, will just note that it's an earthed conduit set up.
Where I get more confused is the R1+R2 measurement seeing as I can't cross-connect the line and CPC at the board... What's the conventional thing to do in this case? Just put a link between the adaptable box where both ends of the conduit terminate and the line conductors then test at each outlet as normal?
Cheers!
ajust link the conduit to the line conductor at DB, then measure between them at whatever points you want. another method would be to use a wander lead an measure R2 ( the conduit alone ).
Reply to Testing RFC in earthed steel conduit... in the UK Electrical Forum area at ElectriciansForums.net