just a quick question I want to clear up, basically when testing a ring circuit, why is it that the ohm values slightly increase per reading, and highest at the centre point?
and by how much does the resistance increase when a cable is connected, say with a terminal block. apposed to say a complete round circuit with no connects, if it as possible to make such a cable, (like the letter O, a complete band , hope u get my drift)
cheers
The reason the ohm value increases is because the cable length is longer which increases the resistance of the cable. And for your second question i havent got a clue.
Luke,
if the readings are increasing, then you are doing it wrong:rolleyes:
step one - end to ends of the phase (r1) neutral (rn) and cpc (r2)
if using 2.5/1.5 twin and earth then r2 is 1.66 times higher value than r1 and rn (because 2.5/1.5 = 1.66)
step 2 cross connect phase and neutral - incoming phase to outgoing neutral and outgoing phase to incoming neutral
measure between phase and neutral at each socket. value should be the same (+-0.05 ohms) with the value being r1+rn divided by 4. If you your valew is increasing then you have connected incoming to incoming, and outgoing to outgoing
step 3 - do same with phase and CPC, value will be r1 + r2 divided by 4, and will be your R1+R2 value for the circuit.
Both step 2 and step 3 readings will increase slightly on spurs.
any junctions boxes or connections that yopu add to the circuit will potentiall add resistance
sorry if i am egg sucking, but i appreciate that some people may be reading this and learning something!!!:eek::)
Reply to Testing Ring Continuity short Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...