hi everyone,
when ir testing a selv lighting circuit if you cant get to the transformers to disconnect the transformers do you test at 250v and test between line&neutral connected together and test between them and earth is that correct
 
Last edited:
I would say that if you are testing the primary side of the transformer then you are testing a low voltage instalation, test as you say, but test at 500v.
 
thanks for reply if i test at 500v this wont damage the transformers will it because of connecting live neutral together do i still have to remove all lamps or can you leave them in place
 
No you will not damage any lamps or the transformers. You are just putting a test voltage between the live conductors and the earth.
 
No you will not damage any lamps or the transformers. You are just putting a test voltage between the live conductors and the earth.
cheers andy thanks for that its for my brother he had it done a while ago but most of house on old wylex fuse board and new kitchen extension sockets and kitchen lights on new but will have to check sockets might be half on original side of kitchen and half on new 12 way split c.c.u.he wants me to transfer all to new c.c.u and tidy it all up if the guy that did it is qualified hes rough as spaghetti jct. he will still have to notify building control wont he as its work on a c.c.u, but before i do any of it i am going to test all old existing circuits to check for faults and stuff looks like the existing water bond is only 6mm and to me it looks like theres damage either been burning or insulation damaged the guy who wired extension should have made that good shouldnt he so going to test it all and upgrade bonding first as im not adding a ccu or installing a new one do i still have notify for transferring all final circuits and getting rid of wylex and hes had all new fitted wardrobes in all bedrooms told him he should have had all house rewired before doing it all up cheers for response so i will only have to test at 250v when testing a selv circuit on secondary side or when testing circuits what have sensitive equipment ie alarms and equipment i cant disconnect or should i always test with line/neutral connected together and test live to earth
 
Last edited:

Reply to testing selv lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
Interesting. Sounds unusual since it seems it was very lightly loaded. Not much you can do I suppose other than buy a replacement unit. Unless...
Replies
7
Views
609

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top