Hi all

just after some guidance on tetsing supp bonding, just want to make sure I am doing the right tests when carrying out condition reports.

I always check to see if i can see if it is present, then if it is not visually present and all circuits are not rcd protected in the bathroom then i will do the resistance calc 50V / Ia

so for example i use the highest rated mcb, usually shower circuit and do the calc, so say for a 40A mcb = 50 / 200 = 0.25 ohms, i then test between all exposed and extraneous conductive parts making sure the reading is less than 0.25 ohms, if not then i code 2 it.

My other question is, if say the shower was rcd protected but the lights were not, would you use the lighting mcb for the calculation and ignore the shower, or still go worst case scenario and use the shower mcb.

Am i doing the right things or am i missing something, sorry if this is basic stuff to some, but the reason i ask as i have just started working with a new guy and he hs been putting doubts in my head, just want to make sure i am doing everything correct.

If anyone has any other methods or anything, i am always welcome to advice, always looking to learn and improve.

Thanks guys
 
make life easy for yourself and ditch all these calcs for an eicr , they're not necessary.
if you cant see any sign of sup bonding its prob not there so just code it.
 

Reply to Testing supp bonding and EICR's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
956
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top