I started to run the Insulation resistance tests @ 250v which most circuits passed with no issues apart from the Ring Main Sockets which. I got a >999 for Neutral to Live but I got a low reading of 112 ohms for Live to Earth. For 500v I got a measurement of 600 ohms Neutral - Live and 120 ohms for Live - Earth. A couple of the other circuits also struggled at 500 volts.
@mackatoon there's something not right here. I don't see how you can be getting those results from an IR test.

IR tests return results in meg ohms. 1 meg ohm = 1,000,000 ohms. 120 ohms would show a reading on your meter of 0.00012 meg ohms. Is that really the reading you got at 500V? My meter only has a resolution of 0.01 meg ohms for IR tests.

I suspect, as @westward10 has suggested, you are confusing meg ohms for ohms.
 
In addition to the logic above which I agree with, it was mentioned that R1+R2 was carried out and was ok, and in my head that simply can't be the case if there's really 120 ohms in parallel between R1 and R2, even at the much lower voltage that test uses. (Might be red herring but was R1+R2 done at board or a socket, and if a socket are you sure everything properly re-terminated)

More generally - it's really easy to get increasingly stressed and for rational judgement to go out of the window when IR tests do strange things. Been there plenty of times! I think it was @westward10 who told me once the results were only getting worse each time due to the increased sweat on my fingers affecting the resistance!
New day, cup of tea (solves most electrical problems) and calmly start again I reckon. Please do report back, you have a bunch of us interested now!
 
Are there any fuse spurs with old neons in? They can often show up poor IR results - as can extension leads with neons (not so much the more modern LED ones).

But the key is to approach it calmly and if getting odd readings try to isolate it.

If there are only 1-2 sockets per room and tenant is using lots of extension leads then a rewire is probably advisable at some point (assuming the wiring is not recent and just stingy with sockets), but that's very different from being necessary on an EICR.
 

Reply to Testing Thoughts in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope you get better soon .sounds quite serious
    • Friendly
    • Like
Replies
12
Views
760
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
806
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
585
Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top