Testing with Motors in Installation | on ElectriciansForums
Discuss Testing with Motors in Installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
J
jamminuk
Hi all,
It suddenly occurred to me that i'm not 100% on how to perform tests with a motor in the circuit :-S damn so many things to remember for the 2391!! Wish it was open book :)
Any help appreciated
Ben
Hi all,
Ben
In effect, you don't test with the motor 'in circuit'.
You'll have a motor starter and test up to the supply side as per usual.
You can then test between the load side of the starter and the motor socket (if this is 2391-10 practical).
Reply to Testing with Motors in Installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!