testing Zs and Ze | on ElectriciansForums
Discuss testing Zs and Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
zone77
Barrow
when i measure Ze from a DB ( disconnecting main bonding) am i suppose to reconnect bonding b4 testing Zs on final circuits. on job 2day some Zs from sockets was lower than Ze:confused:. i put this down to parralell paths but am i doing it correctly??
As soon as you have done Ze reconect main earth before doing any Zs tests ( paralell paths will influence Zs)
Paul
Reply to testing Zs and Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...