:confused:Is there any ruling/guidelines that state that you cannot test for efli of the lighting circuit at the light switch providing your meter does not need a neutral to power it up? as it is easier and often less hassle with light fittings in many houses today?
 
:confused:Is there any ruling/guidelines that state that you cannot test for efli of the lighting circuit at the light switch providing your meter does not need a neutral to power it up? as it is easier and often less hassle with light fittings in many houses today?

well what you have to consider Tony, if you are using presumably a three plate ceiling rose, then the light swtich is not the extremity of your circuit

As you know, the value of R1+R2 and Zs entered on your test results are the HIGHEST reading for each final circuit

If you are three plating then this will be at your rose, not the switch

Consider a 2 way lighting circuit, depending on the configuration, you could be adding 10m-20m easily by the time it goes up and down your strappers

and anyway under the 17th, when more light circuits come under RCD's, if you are measuring on 'no trip loop' or equivalanet, a lot of meters will need that neutral!;)
 
well what you have to consider Tony, if you are using presumably a three plate ceiling rose, then the light swtich is not the extremity of your circuit

As you know, the value of R1+R2 and Zs entered on your test results are the HIGHEST reading for each final circuit

If you are three plating then this will be at your rose, not the switch

Consider a 2 way lighting circuit, depending on the configuration, you could be adding 10m-20m easily by the time it goes up and down your strappers

and anyway under the 17th, when more light circuits come under RCD's, if you are measuring on 'no trip loop' or equivalanet, a lot of meters will need that neutral!;)

cheers pal fair comments
 

Reply to testing Zs at the light switch in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
853
nicebutdim
N
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top