well what you have to consider Tony, if you are using presumably a three plate ceiling rose, then the light swtich is not the extremity of your circuit
As you know, the value of R1+R2 and Zs entered on your test results are the HIGHEST reading for each final circuit
If you are three plating then this will be at your rose, not the switch
Consider a 2 way lighting circuit, depending on the configuration, you could be adding 10m-20m easily by the time it goes up and down your strappers
and anyway under the 17th, when more light circuits come under RCD's, if you are measuring on 'no trip loop' or equivalanet, a lot of meters will need that neutral!