pjb1
Just carried out a periodic inspection report, before doing a Cu change. When the board is replaced can i use the results i obtained and transfer them onto the electrical Installation certificate. Or do i have to test again.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi.
Surely you would re-test....make sure all your work was correct. Also the chracteristics of the circuits will have changed i.e new overload and fault protection so different permitted Zs and RCD operating times.
I always test again.
Don't forget that there maybe a chance of borrowed neutrals which will cause the RCD to trip as well when fitting the new DB
Whilst doing a periodic Inspection, which test would have highlighted the borrowed neutral?
Just asking as i'm still learning and up to now, have passed any PIR work onto other well experienced spark friends.
Wouldn't it be better to have done just the installation tests as board fitted or was board fitted due to failing periodic?Just carried out a periodic inspection report, before doing a Cu change. When the board is replaced can i use the results i obtained and transfer them onto the electrical Installation certificate. Or do i have to test again.
When you are doing your IR tests, its likely that an infinity reading across phase and neutral would suggest a burrowed neutral as its not very often you'll find such a large resistance, unless its a short run of cable. A 20M run of 2.5mm T+E or NYMJ would have a IR of between 1500megs and 2000megs.
if you have carried out..... ins res ,,, conts..... r1 + r2.....tests...( the dead tests )...then these test results shudnt be any diffrent if fitting a new db.... the new dist board tho should have an rcd ,,,so these times will now be required... if you have uprated the earths for water ,,gas & perhaps the main earthing conductor then it maybe a good idea to re-test the live tests...i would personnallyJust carried out a periodic inspection report, before doing a Cu change. When the board is replaced can i use the results i obtained and transfer them onto the electrical Installation certificate. Or do i have to test again.