Hi people I have my niceic approved assessment on the 7th June and just wanted to ask a few simple questions.
1- R1+R2 on lighting circuit, if I have awkward fittings is it still essential to test at them?
2- Do I have to do R1+Rn on every circuit or just the cross connection one on ring?
I'd look in my books but I'm too comfy watching xmen on the sofa!
Thanks
 
1 - R1&R2 will be needed to confirm polarity. If you were to opt for the R2 method or just missing them altogether then you would have to record it accordingly.
2 - R1&RN isn't necessarily required on a new installation for circuits other than the ring final, however if you were carrying out a periodic it would be required for verification of voltage drop purposes.
 
Hi people I have my niceic approved assessment on the 7th June and just wanted to ask a few simple questions.
1- R1+R2 on lighting circuit, if I have awkward fittings is it still essential to test at them?
2- Do I have to do R1+Rn on every circuit or just the cross connection one on ring?
I'd look in my books but I'm too comfy watching xmen on the sofa!
Thanks

Sorry but you sound like a right lazy *******
 
use guidance notes 3 or buy Brian scaddons testing & Inspection.
but on radial you do not need to do r1 rn r1 +r2 allways end on circuit last light from switch Zs from light it self.
sockets do every one highest result recorded beware of results in comparrison to r1 +r2 and Ze
3 remeberr your sequence of testing.
remove all loads
and when you finnish watching Tv i am sure wll read these replies and i have to gree with truckster i think you better hope your area engineer is not reading this either or you could find you will ex nNIC
 

Reply to Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
No live and neutral at the wall. But that would be the switch live right?
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top