Could somebody please tell me how to test resistance of an earth rod in a domestic installation using megger MFT1553?
Thanks
 
ok here we go.

1 First of all totally isolate the installation
2 disconnect the main earth conductor from the main earth terminal.
3 with the tester set to the ZE setting clamp onto the main earth conductor and put your probe into the main incomming phaswe conductor.

you will get a Ze reading. this is your earth rod reading.

remember to re terminate the Main earth conductor before energising the system.

If you look at GN 3 earth rod testing method 2 its a bit clearer.
 
Just to add to what Scotsparky has already said, technically the reading you obtain is referred to as an Ra - as in the equation...

Ra (resistance of earth rod) x I delta n (residual op` current of RCD) must be no greater than 50v (considered safe touch voltage)

It`s thru this formula that we arrive at max permissible value of 1667 ohms for a 30mA protected TT install (altho` we have to aim for something less than 200 ohms)
 

Reply to Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
935
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

It depends very much on what RCD you are using, or even If you are using one. For example, if the RCD is 500mA then a max Ra of 100ohms is classed...
Replies
2
Views
224
what is the piece of equipment and part number?
Replies
9
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top