keefy
Have been asked to make additions to a thatched property. Never worked in one before but quickly noted that the upper floor was wired in SWA!
Is this some insurance requirement? I would have thought FP200 would be better...
Any experienced advice very welcome.
There are often requirements put in place by both insurance companies and Local Authorities.
Then there are recommendations that the local Fire Officer may have.
Best to check.
I'm not aware that BS7671 has any particular requirements for thatched properties.
I believe that it doesn't even consider it to be a special location.
Obviously there are some requirements when choosing equipment and fittings if they are to be installed near to or within the thatch Chapter 42 for instance.
In my part of the world, a thatched property has to be done in steel conduit. I've never done one so I can't be sure.
Did a thatched property not have to be wired in micc?
Best of British on that one!
What about pyro?
Didn't think there was a difference
Doing it in MI would certainly save on rewires in years to come. I worked on a house a few months back that was wired in MI 50 years ago and it's still in good condition
The "Dorset Model" general electrical requirements for alterations or new build thatched properties in Dorset.
Electrical Supply
If the electrical supply is from overhead lines the incoming lines must be spaced 300mm from the thatch.
RCD protection
All circuits in a thatched property should be RCD protected.
Wiring
It is possible to design electrical circuitry so that there is no wiring within the roof space, by having wall mounted instead of ceiling mounted lighting for example, and this is the best option. Do not have recessed ceiling lights on the upper floor, unless separated from the loft by 30 minutes of fire resistance, with allowance made for ventilation to prevent over-heating of the fitting. However, if wiring in the loft cannot then the following precautions are advised to minimise the likelihood of an electrical fault fire.
Squirrels, mice and rats all seem to enjoy gnawing PVC cable. Unless the loft can be made vermin free, which is difficult to guarantee with thatch, wiring should either be contained in conduit, or proof against attack itself, (e.g. steel wired armoured). Fire resisting cables are not necessarily vermin proof as they are not protected by a hard metal sheathing, (copper sheathing is comparatively soft). Metal conduit is satisfactory and good results have been reported with the use of high impact plastic pipe with a minimum diameter of 20mm. Soft plastic, or smaller diameters, would allow penetration by biting and should therefore be avoided.
Any light in the loft should be of the bulkhead or well-glass design, be sited on a central post away from the thatch and have its switch in the landing. Wiring should not be fixed to the side of rafters, to avoid possible penetration by thatching spikes/crooks, and junction boxes should be avoided so that all cable within the roof space is a continuous length.
Smoke Alarms
[FONT=&amp]A domestic mains and battery powered, interlinked smoke alarm system will be required with one smoke alarm fitted in the roof void. The system should generally be in accordance with that specified in Approved Document B.[/FONT]
The ‘Dorset Model’ has been jointly produced by the Local Authorities across Dorset in conjunction with Dorset Fire and Rescue Service, The Dorset Master Thatchers Association and after consultation with the National Inspection Council for Electrical Installation Contracting and the British Research Establishment Ltd. On the basis that evidence has shown that thatch can be made sacrificial in the event of fire.
Mark, I assume from that detailed post it is more to do with rodents creating the dangers of arcing by partly chewing the cables?
Thanks for a fantastic response.
It might be worth checking building regulations aswell as electrical. Where I am lightning protection is also required for thatched properties. It might also be worth checking if it's a listed or heritage building
Reply to Thatched Property rewire in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
day rate or hourly....I prefer hourly and then it stops them moaning if you are ten mins late one day
Had a quick look this morning as it’s local. It’s a full rcbo starbreaker installed in the kitchen pantry but unfortunately it’s plastic...