The customer wants a 2kW heat lamp installed outside.
The existing garage consumer unit is 2 way with no spare ways (16A sockets, 6A lights). I was under the impression that anything 2kW and over needs to be on it's own circuit. However, looking at Fig 15A (iii) in Appendix 15 it states 'exceeding 2kW', in addition this is under the heading for a ring rather than a radial.
The existing 2 way garage CU has a 16A radial, would the 9A heat lamp be suitable for this? The radial feeds 4 sockets in the garage, none of these are in constant use. The chap uses it as a workshop, when he is using it it may well trip if the heat lamp is on, due to overload.
My thoughts are... best practise would still be to fit a new garage consumer unit as it would be poor design utilising the existing CU. However, it doesn't seem to be breaking the regulations, meaning perhaps I have the choice of offering both options to the customer, giving him the facts, and letting him make the choice?
Edit.. It may actually be 2.02kW as it will have a 5w LED light with it! So perhaps it is over 2kW, not on a ring though.
The existing garage consumer unit is 2 way with no spare ways (16A sockets, 6A lights). I was under the impression that anything 2kW and over needs to be on it's own circuit. However, looking at Fig 15A (iii) in Appendix 15 it states 'exceeding 2kW', in addition this is under the heading for a ring rather than a radial.
The existing 2 way garage CU has a 16A radial, would the 9A heat lamp be suitable for this? The radial feeds 4 sockets in the garage, none of these are in constant use. The chap uses it as a workshop, when he is using it it may well trip if the heat lamp is on, due to overload.
My thoughts are... best practise would still be to fit a new garage consumer unit as it would be poor design utilising the existing CU. However, it doesn't seem to be breaking the regulations, meaning perhaps I have the choice of offering both options to the customer, giving him the facts, and letting him make the choice?
Edit.. It may actually be 2.02kW as it will have a 5w LED light with it! So perhaps it is over 2kW, not on a ring though.