The Arcing Neutral | on ElectriciansForums
Discuss The Arcing Neutral in the UK Electrical Forum area at ElectriciansForums.net
South east
Why do the Neutral connections seem to burn out more than the line?
Is it because the Neutral collects more debris, harmonics and all sorts of junk like that?
It seems that the Neutral conductor connections are the ones to watch and I am not sure why.
Any opinions are welcome.
Thanks very much.
Probably people are more diligent on tightening up the line (cos it is dangerous) and not the neutral because there is no voltage on that!
Not really a good answer but cannot really see a effective difference between the two same current in each case but as you say normally the neutral.
That's what I was thinking but didn't dare post it!
Interesting question though.
Yes that is interesting
I went to a job the other day where upstairs lights had gone out, all lights were on one circuit however downstairs still working, anyhow i had a look in the db and to my horror there was 5 cables into the one mcb, and not one was caught tight in the terminal they were purely sat in the back of the mcb
Had been like that for years and not one sign of burning/arcing etc
With three phase systems and dirty neutrals much more emphasis must be placed on neutral continuity.
By dirty I mean.
Switch mode power supplies
VSD’s
It just gets worse the more I think of it.
Gone are the days of 3½ core cable. Now 4 core or even 3&1.5N core are specified.
Progress at what price?
surely if there isn`t a voltage on the neutral then you can get inert currents just sitting there=heat buildup....and in time the difference in expansion and contraction rates of copper V brass/steel will have the effect of causing loose neutrals......but whenever i am terminating multi-stranded conductors....such as tails etc...when i have tightened the terminations....i always manipulate the cable a bit.....usually wants to nip up again after that.....
Thanks to all these new fangled wiz bang machines the calculation for neutral current has gone out of the window. It used to be fairly easy
In = √(Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)).
But now with the higher end harmonics it’s all gone belly up. Even you're average clamp meter will struggle to give a sensible reading.
From what I’ve been reading distribution transformers are suffering particularly in town centers due to high neutral currents, they can reduce the rating by 75%
Reply to The Arcing Neutral in the UK Electrical Forum area at ElectriciansForums.net
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
No live and neutral at the wall. But that would be the switch live right?