Sometimes it's the only way.

let me explain. called out to a MCB tripping when lights ( 9 LED GU10s ) switched on. installation was done by myself 4 years ago. IR test L-N @ 250V read >999Meg. removed 4 lamps, switched on OK. replaced 2, OK. 3rd one in and POP. tripped. QED.
 
Sometimes it's the only way.

Maybe not. In electronic benchwork the bang test can have expensive knock-on effects. E.g. if a dead high-power amplifier or SMPSU has eaten all its power transistors, the next time you run it up after changing them, if you didn't completely clear the underlying fault it will just eat the new ones in milliseconds, wasting ÂŁ100s and hours of work.

The trick is to connect a GLS lamp in series as an automatic ballast. Choose a lamp wattage that will not light under normal conditions, so its resistance remains low leaving most of the 230V across the load under test. But if the consumption is much too high the lamp heats up, its resistance shoots up and throttles the supply to the faulty device usually before anything more goes wrong. It also give a very responsive indication of the load that you can monitor the situation with. The same concept is used in PTC 'solid state fuses' but the lamp is faster and more flexible for testing purposes.

A 100W GLS lamp in series with your LEDs would have remained dark when testing the good ones but lit up harmlessly when the faulty lamp was inserted.
 
Sometimes it's the only way.

let me explain. called out to a MCB tripping when lights ( 9 LED GU10s ) switched on. installation was done by myself 4 years ago. IR test L-N @ 250V read >999Meg. removed 4 lamps, switched on OK. replaced 2, OK. 3rd one in and POP. tripped. QED.

Had exactly the same issue at a place a couple of weeks ago,a faulty GU10 LED was blowing the mcb and had trashed a dimmer. Link switch wires...insert a lamp....breaker on,no bang....breaker off,insert lamp,breaker on.....continue like that till it goes bang,replace faulty lamp....new dimmer....home and beer.
 

Reply to The Bang Test. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
You too? I thought I was in a unique position:anguished::coldsweat:
    • Like
Replies
5
Views
270

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top